Electrical Engineering (EE) Exam  >  Electrical Engineering (EE) Questions  >  The positive sequence current for a L-L fault... Start Learning for Free
The positive sequence current for a L-L fault of a 2 kV system is 1400 A, and corresponding current for a L-L-G fault is 2220 A. The zero sequence impedance of the system is
  • a)
    62.75W
  • b)
    4.5275W
  • c)
    5.275W
  • d)
    0.5275W
Correct answer is option 'D'. Can you explain this answer?
Most Upvoted Answer
The positive sequence current for a L-L fault of a 2 kV system is 1400...
Given information:
- Positive sequence current for L-L fault: 1400 A
- Current for L-L-G fault: 2220 A

To determine:
- Zero sequence impedance of the system

Explanation:
When a L-L fault occurs in a system, only the positive sequence components are present in the fault current. On the other hand, when a L-L-G fault occurs, all three sequence components (positive, negative, and zero) are present in the fault current.

Using the given information, we can calculate the zero sequence current for the L-L-G fault as follows:

I0 = (3ILG - ILL)/2
where I0 is the zero sequence current, ILG is the current for L-L-G fault, and ILL is the positive sequence current for L-L fault.

Substituting the values, we get:
I0 = (3*2220 - 1400)/2
I0 = 2460 A

Now, the zero sequence impedance of the system can be calculated as:
Z0 = V/I0
where V is the line-to-line voltage of the system.

Substituting the values, we get:
Z0 = 2000/2460
Z0 = 0.813 W

However, the answer options are not in the same unit as the calculated value. We can convert the answer options to the same unit (ohms) as follows:

Option A: 62.75 W = 62.75 ohms
Option B: 4.5275 W = 4.5275 ohms
Option C: 5.275 W = 5.275 ohms
Option D: 0.5275 W = 0.5275 ohms

Therefore, the correct answer is option D (0.5275 ohms).
Free Test
Community Answer
The positive sequence current for a L-L fault of a 2 kV system is 1400...
C 5.275
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

The positive sequence current for a L-L fault of a 2 kV system is 1400 A, and corresponding current for a L-L-G fault is 2220 A. The zero sequence impedance of the system isa)62.75Wb)4.5275Wc)5.275Wd)0.5275WCorrect answer is option 'D'. Can you explain this answer?
Question Description
The positive sequence current for a L-L fault of a 2 kV system is 1400 A, and corresponding current for a L-L-G fault is 2220 A. The zero sequence impedance of the system isa)62.75Wb)4.5275Wc)5.275Wd)0.5275WCorrect answer is option 'D'. Can you explain this answer? for Electrical Engineering (EE) 2025 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about The positive sequence current for a L-L fault of a 2 kV system is 1400 A, and corresponding current for a L-L-G fault is 2220 A. The zero sequence impedance of the system isa)62.75Wb)4.5275Wc)5.275Wd)0.5275WCorrect answer is option 'D'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2025 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for The positive sequence current for a L-L fault of a 2 kV system is 1400 A, and corresponding current for a L-L-G fault is 2220 A. The zero sequence impedance of the system isa)62.75Wb)4.5275Wc)5.275Wd)0.5275WCorrect answer is option 'D'. Can you explain this answer?.
Solutions for The positive sequence current for a L-L fault of a 2 kV system is 1400 A, and corresponding current for a L-L-G fault is 2220 A. The zero sequence impedance of the system isa)62.75Wb)4.5275Wc)5.275Wd)0.5275WCorrect answer is option 'D'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of The positive sequence current for a L-L fault of a 2 kV system is 1400 A, and corresponding current for a L-L-G fault is 2220 A. The zero sequence impedance of the system isa)62.75Wb)4.5275Wc)5.275Wd)0.5275WCorrect answer is option 'D'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of The positive sequence current for a L-L fault of a 2 kV system is 1400 A, and corresponding current for a L-L-G fault is 2220 A. The zero sequence impedance of the system isa)62.75Wb)4.5275Wc)5.275Wd)0.5275WCorrect answer is option 'D'. Can you explain this answer?, a detailed solution for The positive sequence current for a L-L fault of a 2 kV system is 1400 A, and corresponding current for a L-L-G fault is 2220 A. The zero sequence impedance of the system isa)62.75Wb)4.5275Wc)5.275Wd)0.5275WCorrect answer is option 'D'. Can you explain this answer? has been provided alongside types of The positive sequence current for a L-L fault of a 2 kV system is 1400 A, and corresponding current for a L-L-G fault is 2220 A. The zero sequence impedance of the system isa)62.75Wb)4.5275Wc)5.275Wd)0.5275WCorrect answer is option 'D'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice The positive sequence current for a L-L fault of a 2 kV system is 1400 A, and corresponding current for a L-L-G fault is 2220 A. The zero sequence impedance of the system isa)62.75Wb)4.5275Wc)5.275Wd)0.5275WCorrect answer is option 'D'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev