A star connected 3 phase, 12 MVA, 8 KV alternator is protected by Merz-Price circulating current principle using 1000/5 amperes current transformers. The start point of the alternator is earthed through a resistance of 10 Ω. If the minimum operating current for the relay is 1 A. Calculate the percentage of each phase of the stator winding which is unprotected against earth-faults when the machine is operating at normal voltage.
    Correct answer is between '40,46'. Can you explain this answer?
    Verified Answer
    A star connected 3 phase, 12 MVA, 8 KV alternator is protected by Merz...
    Let x% of the winding be unprotected.
    Earth resistance, r = 10 Ω
    Voltage per phase, 
    Minimum fault current which will operate the relay =  
    EMF induced in x% winding = 
    = 46.19 x volts
    Earth fault current which x% winding will cause

    ⇒ 4.62x = 200
    ⇒ x = 43.29%
    Hence, 43.29% of alternator winding is left unprotected.
     
    View all questions of this test
    Most Upvoted Answer
    A star connected 3 phase, 12 MVA, 8 KV alternator is protected by Merz...
    Ohms.

    Assuming a balanced three-phase fault occurs on the alternator terminals, the fault current will flow through the 10 ohm resistance to earth, and a circulating current will be induced in the Merz-Price system. The circulating current will be proportional to the fault current and will flow through the CTs, causing the relay to operate.

    Let's calculate the circulating current:

    The fault current can be calculated using the formula:

    I_fault = MVA / (√3 x kV)

    where MVA is the rated power of the alternator and kV is the rated voltage.

    I_fault = 12 x 10^6 / (√3 x 8 x 10^3) = 866.03 A

    The circulating current can be calculated using the formula:

    I_circulating = k x I_fault

    where k is the ratio of the CTs.

    k = 1000 / 5 = 200

    I_circulating = 200 x 866.03 = 173,206 A

    Therefore, if a balanced three-phase fault occurs on the alternator terminals, a circulating current of 173,206 A will flow through the CTs, causing the relay to operate and trip the circuit breaker.
    Explore Courses for Electrical Engineering (EE) exam

    Similar Electrical Engineering (EE) Doubts

    Top Courses for Electrical Engineering (EE)

    A star connected 3 phase, 12 MVA, 8 KV alternator is protected by Merz-Price circulating current principle using 1000/5 amperes current transformers. The start point of the alternator is earthed through a resistance of 10 Ω. If the minimum operating current for the relay is 1 A. Calculate the percentage of each phase of the stator winding which is unprotected against earth-faults when the machine is operating at normal voltage.Correct answer is between '40,46'. Can you explain this answer?
    Question Description
    A star connected 3 phase, 12 MVA, 8 KV alternator is protected by Merz-Price circulating current principle using 1000/5 amperes current transformers. The start point of the alternator is earthed through a resistance of 10 Ω. If the minimum operating current for the relay is 1 A. Calculate the percentage of each phase of the stator winding which is unprotected against earth-faults when the machine is operating at normal voltage.Correct answer is between '40,46'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A star connected 3 phase, 12 MVA, 8 KV alternator is protected by Merz-Price circulating current principle using 1000/5 amperes current transformers. The start point of the alternator is earthed through a resistance of 10 Ω. If the minimum operating current for the relay is 1 A. Calculate the percentage of each phase of the stator winding which is unprotected against earth-faults when the machine is operating at normal voltage.Correct answer is between '40,46'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A star connected 3 phase, 12 MVA, 8 KV alternator is protected by Merz-Price circulating current principle using 1000/5 amperes current transformers. The start point of the alternator is earthed through a resistance of 10 Ω. If the minimum operating current for the relay is 1 A. Calculate the percentage of each phase of the stator winding which is unprotected against earth-faults when the machine is operating at normal voltage.Correct answer is between '40,46'. Can you explain this answer?.
    Solutions for A star connected 3 phase, 12 MVA, 8 KV alternator is protected by Merz-Price circulating current principle using 1000/5 amperes current transformers. The start point of the alternator is earthed through a resistance of 10 Ω. If the minimum operating current for the relay is 1 A. Calculate the percentage of each phase of the stator winding which is unprotected against earth-faults when the machine is operating at normal voltage.Correct answer is between '40,46'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
    Here you can find the meaning of A star connected 3 phase, 12 MVA, 8 KV alternator is protected by Merz-Price circulating current principle using 1000/5 amperes current transformers. The start point of the alternator is earthed through a resistance of 10 Ω. If the minimum operating current for the relay is 1 A. Calculate the percentage of each phase of the stator winding which is unprotected against earth-faults when the machine is operating at normal voltage.Correct answer is between '40,46'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A star connected 3 phase, 12 MVA, 8 KV alternator is protected by Merz-Price circulating current principle using 1000/5 amperes current transformers. The start point of the alternator is earthed through a resistance of 10 Ω. If the minimum operating current for the relay is 1 A. Calculate the percentage of each phase of the stator winding which is unprotected against earth-faults when the machine is operating at normal voltage.Correct answer is between '40,46'. Can you explain this answer?, a detailed solution for A star connected 3 phase, 12 MVA, 8 KV alternator is protected by Merz-Price circulating current principle using 1000/5 amperes current transformers. The start point of the alternator is earthed through a resistance of 10 Ω. If the minimum operating current for the relay is 1 A. Calculate the percentage of each phase of the stator winding which is unprotected against earth-faults when the machine is operating at normal voltage.Correct answer is between '40,46'. Can you explain this answer? has been provided alongside types of A star connected 3 phase, 12 MVA, 8 KV alternator is protected by Merz-Price circulating current principle using 1000/5 amperes current transformers. The start point of the alternator is earthed through a resistance of 10 Ω. If the minimum operating current for the relay is 1 A. Calculate the percentage of each phase of the stator winding which is unprotected against earth-faults when the machine is operating at normal voltage.Correct answer is between '40,46'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A star connected 3 phase, 12 MVA, 8 KV alternator is protected by Merz-Price circulating current principle using 1000/5 amperes current transformers. The start point of the alternator is earthed through a resistance of 10 Ω. If the minimum operating current for the relay is 1 A. Calculate the percentage of each phase of the stator winding which is unprotected against earth-faults when the machine is operating at normal voltage.Correct answer is between '40,46'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Explore Courses
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev