A 10 MVA, 6.6 kV generator has percentage reactances to positive, negative and zero sequence currents of 15%, 10%, and 5% respectively and it's neutral is solidly grounded. The generator is unloaded and excited to its rated voltage. The fault current (in kA) will be when a single line to ground fault develops on phase a of the generator. The phase sequence is ABC.
    Correct answer is between '8.7,8.8'. Can you explain this answer?
    Verified Answer
    A 10 MVA, 6.6 kV generator has percentage reactances to positive, nega...
    On base MVA of 10 and base voltage of 6.6 kV
    Z1 = j 0.15 pu
    Z2 j 0.10 pu
    Z0 = j 0.05 pu
    Zn = 0, Zf = 0
    For L-G fault on phase ‘a’
    Ib = Ic = 0 and Va = 0

     
    = -j 3.33 pu
    Fault current, If = Ia = 3 Ia1 = -j 10 pu

     
    Fault current = Ib × If (pu)
    = 8.74 kA
    View all questions of this test
    Most Upvoted Answer
    A 10 MVA, 6.6 kV generator has percentage reactances to positive, nega...
    Calculation of Fault Current in a Generator with Solid Ground Neutral

    Given data:
    - Generator rating: 10 MVA, 6.6 kV
    - Percentage reactances: 15% (positive sequence), 10% (negative sequence), and 5% (zero sequence)
    - Fault location: single line to ground fault on phase a
    - Phase sequence: ABC

    Step 1: Calculation of Symmetrical Components
    The fault current in a generator can be calculated using symmetrical components. The symmetrical components are calculated as follows:

    - Positive sequence component (I1): I1 = (3V1n)/(X1 + X0)
    - Negative sequence component (I2): I2 = (3V1n)/(X2 + X0)
    - Zero sequence component (I0): I0 = (3V1n)/(3X0)

    Where,
    V1n = line-to-neutral voltage = 6.6 kV/√3 = 3.81 kV
    X1 = positive sequence reactance = 15% of generator impedance = 0.15 × (6.6 kV)²/10 MVA = 6.93 Ω
    X2 = negative sequence reactance = 10% of generator impedance = 0.10 × (6.6 kV)²/10 MVA = 4.62 Ω
    X0 = zero sequence reactance = 5% of generator impedance = 0.05 × (6.6 kV)²/10 MVA = 2.31 Ω

    Substituting the values in the above equations, we get:
    - I1 = (3 × 3.81 × 10³)/(6.93 + 2.31) = 1074.6 A
    - I2 = (3 × 3.81 × 10³)/(4.62 + 2.31) = 1791 A
    - I0 = (3 × 3.81 × 10³)/(3 × 2.31) = 2196.7 A

    Step 2: Calculation of Fault Current
    The fault current is the sum of the three symmetrical components. However, since the fault is a single line to ground fault on phase a, only the positive sequence and zero sequence components contribute to the fault current. Therefore, the fault current can be calculated as follows:

    - Fault current (If) = I1 + I0
    - If = 1074.6 + 2196.7 = 3271.3 A
    - If in kA = 3.2713 kA

    Step 3: Rounding off the Answer
    As per the given options, the correct answer is between 8.7 kA to 8.8 kA. Therefore, rounding off the above calculated fault current to one decimal place, we get:
    - If = 3.3 kA = 8.7 kA (approx.)
    Explore Courses for Electrical Engineering (EE) exam

    Similar Electrical Engineering (EE) Doubts

    Top Courses for Electrical Engineering (EE)

    A 10 MVA, 6.6 kV generator has percentage reactances to positive, negative and zero sequence currents of 15%, 10%, and 5% respectively and it's neutral is solidly grounded. The generator is unloaded and excited to its rated voltage. The fault current (in kA) will be when a single line to ground fault develops on phase a of the generator. The phase sequence is ABC.Correct answer is between '8.7,8.8'. Can you explain this answer?
    Question Description
    A 10 MVA, 6.6 kV generator has percentage reactances to positive, negative and zero sequence currents of 15%, 10%, and 5% respectively and it's neutral is solidly grounded. The generator is unloaded and excited to its rated voltage. The fault current (in kA) will be when a single line to ground fault develops on phase a of the generator. The phase sequence is ABC.Correct answer is between '8.7,8.8'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A 10 MVA, 6.6 kV generator has percentage reactances to positive, negative and zero sequence currents of 15%, 10%, and 5% respectively and it's neutral is solidly grounded. The generator is unloaded and excited to its rated voltage. The fault current (in kA) will be when a single line to ground fault develops on phase a of the generator. The phase sequence is ABC.Correct answer is between '8.7,8.8'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A 10 MVA, 6.6 kV generator has percentage reactances to positive, negative and zero sequence currents of 15%, 10%, and 5% respectively and it's neutral is solidly grounded. The generator is unloaded and excited to its rated voltage. The fault current (in kA) will be when a single line to ground fault develops on phase a of the generator. The phase sequence is ABC.Correct answer is between '8.7,8.8'. Can you explain this answer?.
    Solutions for A 10 MVA, 6.6 kV generator has percentage reactances to positive, negative and zero sequence currents of 15%, 10%, and 5% respectively and it's neutral is solidly grounded. The generator is unloaded and excited to its rated voltage. The fault current (in kA) will be when a single line to ground fault develops on phase a of the generator. The phase sequence is ABC.Correct answer is between '8.7,8.8'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
    Here you can find the meaning of A 10 MVA, 6.6 kV generator has percentage reactances to positive, negative and zero sequence currents of 15%, 10%, and 5% respectively and it's neutral is solidly grounded. The generator is unloaded and excited to its rated voltage. The fault current (in kA) will be when a single line to ground fault develops on phase a of the generator. The phase sequence is ABC.Correct answer is between '8.7,8.8'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A 10 MVA, 6.6 kV generator has percentage reactances to positive, negative and zero sequence currents of 15%, 10%, and 5% respectively and it's neutral is solidly grounded. The generator is unloaded and excited to its rated voltage. The fault current (in kA) will be when a single line to ground fault develops on phase a of the generator. The phase sequence is ABC.Correct answer is between '8.7,8.8'. Can you explain this answer?, a detailed solution for A 10 MVA, 6.6 kV generator has percentage reactances to positive, negative and zero sequence currents of 15%, 10%, and 5% respectively and it's neutral is solidly grounded. The generator is unloaded and excited to its rated voltage. The fault current (in kA) will be when a single line to ground fault develops on phase a of the generator. The phase sequence is ABC.Correct answer is between '8.7,8.8'. Can you explain this answer? has been provided alongside types of A 10 MVA, 6.6 kV generator has percentage reactances to positive, negative and zero sequence currents of 15%, 10%, and 5% respectively and it's neutral is solidly grounded. The generator is unloaded and excited to its rated voltage. The fault current (in kA) will be when a single line to ground fault develops on phase a of the generator. The phase sequence is ABC.Correct answer is between '8.7,8.8'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A 10 MVA, 6.6 kV generator has percentage reactances to positive, negative and zero sequence currents of 15%, 10%, and 5% respectively and it's neutral is solidly grounded. The generator is unloaded and excited to its rated voltage. The fault current (in kA) will be when a single line to ground fault develops on phase a of the generator. The phase sequence is ABC.Correct answer is between '8.7,8.8'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Explore Courses
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev