A 600 kVA transformer has an efficiency of 95% at full load and also at 60% of full load; both at U.P.F. Determine the efficiency of transformer at 3/4 th full load.
    Correct answer is between '95,96'. Can you explain this answer?
    Verified Answer
    A 600 kVA transformer has an efficiency of 95% at full load and also a...

    Salving equs (1) and (2) we get
    Pi = 11.846
    Pc = 19.734
    at 3/4 th full load.
    View all questions of this test
    Most Upvoted Answer
    A 600 kVA transformer has an efficiency of 95% at full load and also a...
    Given data:
    - Transformer rating: 600 kVA
    - Efficiency at full load and 60% load: 95%
    - Power factor: Unity

    Efficiency of transformer at 3/4th full load
    - 3/4th full load means the transformer is handling 450 kVA power (75% of 600 kVA)
    - Let's assume the input power to the transformer at 3/4th full load is Pin
    - Output power at 3/4th full load will be Pout = 0.95 x Pin (since efficiency is given as 95%)
    - At unity power factor, the input power and output power are same, so Pin = Pout
    - Therefore, Pin = Pout = 0.95 x Pin
    - Solving the above equation, we get Pin = 947.37 kVA
    - Input power at 3/4th full load is 947.37 kVA
    - Output power at 3/4th full load is Pout = 0.95 x 947.37 = 899 kVA
    - Efficiency at 3/4th full load = Pout/Pin x 100% = 899/947.37 x 100% = 94.9%
    - Rounded off to nearest integer, efficiency at 3/4th full load = 95%
    - Therefore, the correct answer is between 95 and 96.

    Conclusion:
    - The efficiency of a transformer at different load levels can be calculated using the formula Efficiency = (Output power/Input power) x 100%
    - Efficiency at any load level can be calculated if efficiency at full load and one other load level is given.
    - In this case, we used the given efficiency values at full load and 60% load to calculate the efficiency at 3/4th full load.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    A 600 kVA transformer has an efficiency of 95% at full load and also at 60% of full load; both at U.P.F. Determine the efficiency of transformer at 3/4 th full load.Correct answer is between '95,96'. Can you explain this answer?
    Question Description
    A 600 kVA transformer has an efficiency of 95% at full load and also at 60% of full load; both at U.P.F. Determine the efficiency of transformer at 3/4 th full load.Correct answer is between '95,96'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A 600 kVA transformer has an efficiency of 95% at full load and also at 60% of full load; both at U.P.F. Determine the efficiency of transformer at 3/4 th full load.Correct answer is between '95,96'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A 600 kVA transformer has an efficiency of 95% at full load and also at 60% of full load; both at U.P.F. Determine the efficiency of transformer at 3/4 th full load.Correct answer is between '95,96'. Can you explain this answer?.
    Solutions for A 600 kVA transformer has an efficiency of 95% at full load and also at 60% of full load; both at U.P.F. Determine the efficiency of transformer at 3/4 th full load.Correct answer is between '95,96'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
    Here you can find the meaning of A 600 kVA transformer has an efficiency of 95% at full load and also at 60% of full load; both at U.P.F. Determine the efficiency of transformer at 3/4 th full load.Correct answer is between '95,96'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A 600 kVA transformer has an efficiency of 95% at full load and also at 60% of full load; both at U.P.F. Determine the efficiency of transformer at 3/4 th full load.Correct answer is between '95,96'. Can you explain this answer?, a detailed solution for A 600 kVA transformer has an efficiency of 95% at full load and also at 60% of full load; both at U.P.F. Determine the efficiency of transformer at 3/4 th full load.Correct answer is between '95,96'. Can you explain this answer? has been provided alongside types of A 600 kVA transformer has an efficiency of 95% at full load and also at 60% of full load; both at U.P.F. Determine the efficiency of transformer at 3/4 th full load.Correct answer is between '95,96'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A 600 kVA transformer has an efficiency of 95% at full load and also at 60% of full load; both at U.P.F. Determine the efficiency of transformer at 3/4 th full load.Correct answer is between '95,96'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Explore Courses
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev