A 50-kVA transformer has maximum efficiency of 96 % when delivers 60 % of full load at unity power factor.The iron loss and copper loss at half load in kW a) 0.625-kW, 1.736-kW. b) 0.3125-kW, 0.4340-kW. c) 0.625-kW, 0.4340-kW. d) 0.3125-kW, 0.3125-kW.?
Most Upvoted Answer
A 50-kVA transformer has maximum efficiency of 96 % when delivers 60 %...
Answer:

Given data:

• Transformer rating (S) = 50 kVA
• Maximum efficiency (η) = 96%
• Load (P) = 60% of full load
• Power factor (pf) = 1 (unity)
• Iron loss (Pi) = ?
• Copper loss (Pc) at half load = ?

Efficiency Formula:
Efficiency (η) = Output Power (Pout) / Input Power (Pin)

Output Power Formula:
Pout = S * P * pf

Input Power Formula:
Pin = Pout + Pi + Pc

Calculation of Output Power (Pout):
Pout = S * P * pf
= 50 * 0.6 * 1
= 30 kVA

Calculation of Input Power (Pin):
Using Efficiency Formula,
η = Pout/Pin
0.96 = 30/Pin
Pin = 31.25 kVA

Calculation of Copper Loss (Pc):
Let x be the copper loss at full load.
At half load, copper loss (Pc) is proportional to the square of the load current (I^2).
Therefore, Pc = (0.5)^2 * x
= 0.25x

Calculation of Iron Loss (Pi):
Using Input Power formula,
Pin = Pout + Pi + Pc
31.25 = 30 + Pi + 0.25x
Pi + 0.25x = 1.25

At full load, copper loss (Pc) is equal to x.
Using the given data (60% of full load), the load current is 0.6 times the full load current (I).
Copper loss at 60% of full load (Pc1) is proportional to the square of the load current (I^2).
Therefore, Pc1 = (0.6I)^2 * x
= 0.36x

Using the given data, we have:
η = 96%
Pf = 1
Therefore, the transformer is operating at near unity power factor.
Hence, we can assume that the iron loss (Pi) remains constant for both half load and 60% of full load.

Using the above equations, we get:
Pi + 0.25x = 1.25 ---(1)
x = Pc / 0.25 = 4Pc ---(2)
Pc1 + Pi = 0.6^2 x + Pi = 0.36x + Pi ---(3)

Substituting (2) in (1), we get:
Pi + 0.25 * 4Pc = 1.25
Pi + Pc = 5

Substituting (3) in the above equation, we get:
0.36x + Pi + Pi = 5
0.36x + 2Pi = 5

Using the above equations, we get:
Pi = 0.625 kW
x = 1.736 kW
Pc = 0.434 kW

Therefore, the iron loss and copper loss at half load are 0.625 kW and 0.434 kW respectively.

Hence, the correct option is (c) 0.625-kW, 0.4340-kW.
Community Answer
A 50-kVA transformer has maximum efficiency of 96 % when delivers 60 %...
A
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

A 50-kVA transformer has maximum efficiency of 96 % when delivers 60 % of full load at unity power factor.The iron loss and copper loss at half load in kW a) 0.625-kW, 1.736-kW. b) 0.3125-kW, 0.4340-kW. c) 0.625-kW, 0.4340-kW. d) 0.3125-kW, 0.3125-kW.?
Question Description
A 50-kVA transformer has maximum efficiency of 96 % when delivers 60 % of full load at unity power factor.The iron loss and copper loss at half load in kW a) 0.625-kW, 1.736-kW. b) 0.3125-kW, 0.4340-kW. c) 0.625-kW, 0.4340-kW. d) 0.3125-kW, 0.3125-kW.? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A 50-kVA transformer has maximum efficiency of 96 % when delivers 60 % of full load at unity power factor.The iron loss and copper loss at half load in kW a) 0.625-kW, 1.736-kW. b) 0.3125-kW, 0.4340-kW. c) 0.625-kW, 0.4340-kW. d) 0.3125-kW, 0.3125-kW.? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A 50-kVA transformer has maximum efficiency of 96 % when delivers 60 % of full load at unity power factor.The iron loss and copper loss at half load in kW a) 0.625-kW, 1.736-kW. b) 0.3125-kW, 0.4340-kW. c) 0.625-kW, 0.4340-kW. d) 0.3125-kW, 0.3125-kW.?.
Solutions for A 50-kVA transformer has maximum efficiency of 96 % when delivers 60 % of full load at unity power factor.The iron loss and copper loss at half load in kW a) 0.625-kW, 1.736-kW. b) 0.3125-kW, 0.4340-kW. c) 0.625-kW, 0.4340-kW. d) 0.3125-kW, 0.3125-kW.? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of A 50-kVA transformer has maximum efficiency of 96 % when delivers 60 % of full load at unity power factor.The iron loss and copper loss at half load in kW a) 0.625-kW, 1.736-kW. b) 0.3125-kW, 0.4340-kW. c) 0.625-kW, 0.4340-kW. d) 0.3125-kW, 0.3125-kW.? defined & explained in the simplest way possible. Besides giving the explanation of A 50-kVA transformer has maximum efficiency of 96 % when delivers 60 % of full load at unity power factor.The iron loss and copper loss at half load in kW a) 0.625-kW, 1.736-kW. b) 0.3125-kW, 0.4340-kW. c) 0.625-kW, 0.4340-kW. d) 0.3125-kW, 0.3125-kW.?, a detailed solution for A 50-kVA transformer has maximum efficiency of 96 % when delivers 60 % of full load at unity power factor.The iron loss and copper loss at half load in kW a) 0.625-kW, 1.736-kW. b) 0.3125-kW, 0.4340-kW. c) 0.625-kW, 0.4340-kW. d) 0.3125-kW, 0.3125-kW.? has been provided alongside types of A 50-kVA transformer has maximum efficiency of 96 % when delivers 60 % of full load at unity power factor.The iron loss and copper loss at half load in kW a) 0.625-kW, 1.736-kW. b) 0.3125-kW, 0.4340-kW. c) 0.625-kW, 0.4340-kW. d) 0.3125-kW, 0.3125-kW.? theory, EduRev gives you an ample number of questions to practice A 50-kVA transformer has maximum efficiency of 96 % when delivers 60 % of full load at unity power factor.The iron loss and copper loss at half load in kW a) 0.625-kW, 1.736-kW. b) 0.3125-kW, 0.4340-kW. c) 0.625-kW, 0.4340-kW. d) 0.3125-kW, 0.3125-kW.? tests, examples and also practice Electrical Engineering (EE) tests.