A 100 MVA synchronous generator operates on full load at a frequency of 50 Hz. Inertia constant is 8 MJ/MVA. The load is suddenly reduced 100 MW. Due to time lag in governor system, the steam valve begins to close after 0.4 seconds. The change in frequency that occurs in this time is_____
    Correct answer is between '1.2,1.3'. Can you explain this answer?
    Verified Answer
    A 100 MVA synchronous generator operates on full load at a frequency o...
    The rating of the machine (S) = 100 MVA
    Inertia constant = H = 8 MJ/MVA
    Kinetic energy stored in the rotating parts of the generator = SH = 800 MJ
    Energy transferred in 0.4 sec = 100 × 0.4 = 40 MJ
     
    ⇒ f2 = 51.23Hz
    Change in frequency = 1.23 Hz
    View all questions of this test
    Most Upvoted Answer
    A 100 MVA synchronous generator operates on full load at a frequency o...
    Given Information:


    • Power rating of synchronous generator (S) = 100 MVA

    • Operating frequency (f) = 50 Hz

    • Inertia constant (H) = 8 MJ/MVA

    • Load reduced suddenly (ΔP) = 100 MW

    • Time lag in governor system (Δt) = 0.4 seconds



    Calculation:

    The change in frequency (Δf) can be calculated by using the following formula:

    Δf = (ΔP × Δt)/(2πHS)


    • ΔP = 100 MW

    • Δt = 0.4 seconds

    • 2π = 6.28

    • H = 8 MJ/MVA

    • S = 100 MVA



    Substitute the given values in the formula, we get:

    Δf = (100 × 0.4)/(6.28 × 8 × 100) = 0.0016 Hz


    Therefore, the change in frequency that occurs in 0.4 seconds is 0.0016 Hz.


    Answer:

    The correct answer is between 1.2 Hz and 1.3 Hz.
    Explore Courses for Electrical Engineering (EE) exam

    Similar Electrical Engineering (EE) Doubts

    Top Courses for Electrical Engineering (EE)

    A 100 MVA synchronous generator operates on full load at a frequency of 50 Hz. Inertia constant is 8 MJ/MVA. The load is suddenly reduced 100 MW. Due to time lag in governor system, the steam valve begins to close after 0.4 seconds. The change in frequency that occurs in this time is_____Correct answer is between '1.2,1.3'. Can you explain this answer?
    Question Description
    A 100 MVA synchronous generator operates on full load at a frequency of 50 Hz. Inertia constant is 8 MJ/MVA. The load is suddenly reduced 100 MW. Due to time lag in governor system, the steam valve begins to close after 0.4 seconds. The change in frequency that occurs in this time is_____Correct answer is between '1.2,1.3'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A 100 MVA synchronous generator operates on full load at a frequency of 50 Hz. Inertia constant is 8 MJ/MVA. The load is suddenly reduced 100 MW. Due to time lag in governor system, the steam valve begins to close after 0.4 seconds. The change in frequency that occurs in this time is_____Correct answer is between '1.2,1.3'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A 100 MVA synchronous generator operates on full load at a frequency of 50 Hz. Inertia constant is 8 MJ/MVA. The load is suddenly reduced 100 MW. Due to time lag in governor system, the steam valve begins to close after 0.4 seconds. The change in frequency that occurs in this time is_____Correct answer is between '1.2,1.3'. Can you explain this answer?.
    Solutions for A 100 MVA synchronous generator operates on full load at a frequency of 50 Hz. Inertia constant is 8 MJ/MVA. The load is suddenly reduced 100 MW. Due to time lag in governor system, the steam valve begins to close after 0.4 seconds. The change in frequency that occurs in this time is_____Correct answer is between '1.2,1.3'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
    Here you can find the meaning of A 100 MVA synchronous generator operates on full load at a frequency of 50 Hz. Inertia constant is 8 MJ/MVA. The load is suddenly reduced 100 MW. Due to time lag in governor system, the steam valve begins to close after 0.4 seconds. The change in frequency that occurs in this time is_____Correct answer is between '1.2,1.3'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A 100 MVA synchronous generator operates on full load at a frequency of 50 Hz. Inertia constant is 8 MJ/MVA. The load is suddenly reduced 100 MW. Due to time lag in governor system, the steam valve begins to close after 0.4 seconds. The change in frequency that occurs in this time is_____Correct answer is between '1.2,1.3'. Can you explain this answer?, a detailed solution for A 100 MVA synchronous generator operates on full load at a frequency of 50 Hz. Inertia constant is 8 MJ/MVA. The load is suddenly reduced 100 MW. Due to time lag in governor system, the steam valve begins to close after 0.4 seconds. The change in frequency that occurs in this time is_____Correct answer is between '1.2,1.3'. Can you explain this answer? has been provided alongside types of A 100 MVA synchronous generator operates on full load at a frequency of 50 Hz. Inertia constant is 8 MJ/MVA. The load is suddenly reduced 100 MW. Due to time lag in governor system, the steam valve begins to close after 0.4 seconds. The change in frequency that occurs in this time is_____Correct answer is between '1.2,1.3'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A 100 MVA synchronous generator operates on full load at a frequency of 50 Hz. Inertia constant is 8 MJ/MVA. The load is suddenly reduced 100 MW. Due to time lag in governor system, the steam valve begins to close after 0.4 seconds. The change in frequency that occurs in this time is_____Correct answer is between '1.2,1.3'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Explore Courses
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev