A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactances of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG fault and that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance in ohms (round off to one decimal place) is ___________.
    Correct answer is '1.8Ω'. Can you explain this answer?
    Verified Answer
    A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero ...
    Fault current for SLG fault

    Fault current for 3φ fault

    Xn = 0.1 Pu
    Xn (inΩ) =
    Xn (inΩ) = 1.8Ω  
    View all questions of this test
    Most Upvoted Answer
    A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero ...
    Given information:
    - Voltage rating (V) of generator = 30 kV
    - Frequency (f) of generator = 50 Hz
    - Apparent power (S) of generator = 50 MVA
    - Positive sequence reactance (X1) = 0.25 pu
    - Negative sequence reactance (X2) = 0.15 pu
    - Zero sequence reactance (X0) = 0.05 pu
    - Fault types considered: bolted LG fault and bolted three-phase fault
    - Fault current for both faults is to be equal at the generator terminal
    - Grounding reactance value to be determined

    Calculation steps:
    1. Calculate the per-unit (pu) impedance of the generator using its apparent power and voltage rating:
    Zbase = V^2 / S
    Zbase = (30 kV)^2 / 50 MVA
    Zbase = 18 Ω
    Z1 = X1 * Zbase = 0.25 * 18 Ω = 4.5 Ω
    Z2 = X2 * Zbase = 0.15 * 18 Ω = 2.7 Ω
    Z0 = X0 * Zbase = 0.05 * 18 Ω = 0.9 Ω

    2. Determine the fault current for a bolted LG fault at the generator terminal:
    Ilg = V / Z1
    Ilg = 30 kV / 4.5 Ω
    Ilg = 6.67 kA

    3. Determine the fault current for a bolted three-phase fault at the generator terminal:
    I3φ = V / Z0
    I3φ = 30 kV / 0.9 Ω
    I3φ = 33.33 kA

    4. Set the fault currents for both faults equal to each other and solve for the grounding reactance:
    Ilg = I3φ
    V / Z1 = V / Z0 + 3 * V / Zg
    Zg = 3 * Z1 * Z0 / (3 * Z1 - Z0)
    Zg = 3 * 4.5 Ω * 0.9 Ω / (3 * 4.5 Ω - 0.9 Ω)
    Zg = 1.8 Ω (rounded to one decimal place)

    5. Therefore, the value of grounding reactance in ohms is 1.8 Ω.

    Conclusion:
    The value of grounding reactance is calculated to be 1.8 Ω so that the fault current for a bolted LG fault and that of a bolted three-phase fault at the generator terminal are equal.
    Explore Courses for Electrical Engineering (EE) exam

    Similar Electrical Engineering (EE) Doubts

    Top Courses for Electrical Engineering (EE)

    A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactances of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG faultand that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance in ohms (round off to one decimal place) is ___________.Correct answer is '1.8Ω'. Can you explain this answer?
    Question Description
    A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactances of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG faultand that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance in ohms (round off to one decimal place) is ___________.Correct answer is '1.8Ω'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactances of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG faultand that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance in ohms (round off to one decimal place) is ___________.Correct answer is '1.8Ω'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactances of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG faultand that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance in ohms (round off to one decimal place) is ___________.Correct answer is '1.8Ω'. Can you explain this answer?.
    Solutions for A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactances of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG faultand that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance in ohms (round off to one decimal place) is ___________.Correct answer is '1.8Ω'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
    Here you can find the meaning of A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactances of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG faultand that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance in ohms (round off to one decimal place) is ___________.Correct answer is '1.8Ω'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactances of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG faultand that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance in ohms (round off to one decimal place) is ___________.Correct answer is '1.8Ω'. Can you explain this answer?, a detailed solution for A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactances of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG faultand that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance in ohms (round off to one decimal place) is ___________.Correct answer is '1.8Ω'. Can you explain this answer? has been provided alongside types of A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactances of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG faultand that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance in ohms (round off to one decimal place) is ___________.Correct answer is '1.8Ω'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactances of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG faultand that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance in ohms (round off to one decimal place) is ___________.Correct answer is '1.8Ω'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Explore Courses
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev