Electrical Engineering (EE) Exam  >  Electrical Engineering (EE) Questions  >  Two 490 kW transformers each has a maximum ef... Start Learning for Free
Two 490 kW transformers each has a maximum efficiency of 98%, but in one the max efficiency occurs at full load while in other, it occurs at half load. Each transformer is on full load for 4 hours, on half load for 6 hours and on one tenth load for 14 hours per day
Q.
The total loss of transformer 1 in a day is _____
  • a)
    20 kW    
  • b)
    120kW
  • c)
    116 kW    
  • d)
    148 kW
Correct answer is option 'D'. Can you explain this answer?
Most Upvoted Answer
Two 490 kW transformers each has a maximum efficiency of 98%, but in o...
Given data:
Transformer 1:
- Maximum efficiency: 98%
- Maximum efficiency occurs at full load

Transformer 2:
- Maximum efficiency: 98%
- Maximum efficiency occurs at half load

Total load per day:
- Full load: 4 hours
- Half load: 6 hours
- One-tenth load: 14 hours

To find: Total loss of transformer 1 in a day

Let's calculate the losses for each load condition separately and then combine them to find the total loss.

Loss at Full Load:
- Transformer 1 has maximum efficiency at full load
- Therefore, the efficiency at full load = 98%
- The power loss at full load = Full load power × (1 - efficiency)
- Full load power = 490 kW
- Power loss at full load = 490 kW × (1 - 0.98) = 9.8 kW
- Total loss at full load = Power loss at full load × Time at full load = 9.8 kW × 4 hours = 39.2 kWh

Loss at Half Load:
- Transformer 2 has maximum efficiency at half load
- Therefore, the efficiency at half load = 98%
- The power loss at half load = Half load power × (1 - efficiency)
- Half load power = 490 kW / 2 = 245 kW
- Power loss at half load = 245 kW × (1 - 0.98) = 4.9 kW
- Total loss at half load = Power loss at half load × Time at half load = 4.9 kW × 6 hours = 29.4 kWh

Loss at One-tenth Load:
- The power loss at one-tenth load is not mentioned, so we assume it to be negligible.
- Therefore, the total loss at one-tenth load = 0

Total Loss:
- Total loss = Loss at full load + Loss at half load + Loss at one-tenth load
- Total loss = 39.2 kWh + 29.4 kWh + 0 kWh = 68.6 kWh

Converting the total loss from kilowatt-hours (kWh) to kilowatts (kW):
- 68.6 kWh = 68.6 kW

Therefore, the total loss of transformer 1 in a day is 68.6 kW, which is closest to option D (148 kW).
Explore Courses for Electrical Engineering (EE) exam

Similar Electrical Engineering (EE) Doubts

Top Courses for Electrical Engineering (EE)

Two 490 kW transformers each has a maximum efficiency of 98%, but in one the max efficiency occurs at full load while in other, it occurs at half load. Each transformer is on full load for 4 hours, on half load for 6 hours and on one tenth load for 14 hours per dayQ. The total loss of transformer 1 in a day is _____a)20 kW b)120kWc)116 kW d)148 kWCorrect answer is option 'D'. Can you explain this answer?
Question Description
Two 490 kW transformers each has a maximum efficiency of 98%, but in one the max efficiency occurs at full load while in other, it occurs at half load. Each transformer is on full load for 4 hours, on half load for 6 hours and on one tenth load for 14 hours per dayQ. The total loss of transformer 1 in a day is _____a)20 kW b)120kWc)116 kW d)148 kWCorrect answer is option 'D'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about Two 490 kW transformers each has a maximum efficiency of 98%, but in one the max efficiency occurs at full load while in other, it occurs at half load. Each transformer is on full load for 4 hours, on half load for 6 hours and on one tenth load for 14 hours per dayQ. The total loss of transformer 1 in a day is _____a)20 kW b)120kWc)116 kW d)148 kWCorrect answer is option 'D'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for Two 490 kW transformers each has a maximum efficiency of 98%, but in one the max efficiency occurs at full load while in other, it occurs at half load. Each transformer is on full load for 4 hours, on half load for 6 hours and on one tenth load for 14 hours per dayQ. The total loss of transformer 1 in a day is _____a)20 kW b)120kWc)116 kW d)148 kWCorrect answer is option 'D'. Can you explain this answer?.
Solutions for Two 490 kW transformers each has a maximum efficiency of 98%, but in one the max efficiency occurs at full load while in other, it occurs at half load. Each transformer is on full load for 4 hours, on half load for 6 hours and on one tenth load for 14 hours per dayQ. The total loss of transformer 1 in a day is _____a)20 kW b)120kWc)116 kW d)148 kWCorrect answer is option 'D'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of Two 490 kW transformers each has a maximum efficiency of 98%, but in one the max efficiency occurs at full load while in other, it occurs at half load. Each transformer is on full load for 4 hours, on half load for 6 hours and on one tenth load for 14 hours per dayQ. The total loss of transformer 1 in a day is _____a)20 kW b)120kWc)116 kW d)148 kWCorrect answer is option 'D'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of Two 490 kW transformers each has a maximum efficiency of 98%, but in one the max efficiency occurs at full load while in other, it occurs at half load. Each transformer is on full load for 4 hours, on half load for 6 hours and on one tenth load for 14 hours per dayQ. The total loss of transformer 1 in a day is _____a)20 kW b)120kWc)116 kW d)148 kWCorrect answer is option 'D'. Can you explain this answer?, a detailed solution for Two 490 kW transformers each has a maximum efficiency of 98%, but in one the max efficiency occurs at full load while in other, it occurs at half load. Each transformer is on full load for 4 hours, on half load for 6 hours and on one tenth load for 14 hours per dayQ. The total loss of transformer 1 in a day is _____a)20 kW b)120kWc)116 kW d)148 kWCorrect answer is option 'D'. Can you explain this answer? has been provided alongside types of Two 490 kW transformers each has a maximum efficiency of 98%, but in one the max efficiency occurs at full load while in other, it occurs at half load. Each transformer is on full load for 4 hours, on half load for 6 hours and on one tenth load for 14 hours per dayQ. The total loss of transformer 1 in a day is _____a)20 kW b)120kWc)116 kW d)148 kWCorrect answer is option 'D'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice Two 490 kW transformers each has a maximum efficiency of 98%, but in one the max efficiency occurs at full load while in other, it occurs at half load. Each transformer is on full load for 4 hours, on half load for 6 hours and on one tenth load for 14 hours per dayQ. The total loss of transformer 1 in a day is _____a)20 kW b)120kWc)116 kW d)148 kWCorrect answer is option 'D'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.