A load is supplied by a 230 V, 50 Hz source. The active power P and the reactive power Q consumed by the load are such that 1 kW ≤ P ≤ 2kW and 1 kVAR ≤ Q ≤ kVAR . A capacitor connected across the load for power factor correction generates 1 kVAR reactive power. The worst case power factor after power factor correction is
  • a)
    0.447 lag
  • b)
    0.707 lag
  • c)
    0.894 lag
  • d)
    1
Correct answer is option 'B'. Can you explain this answer?
Verified Answer
A load is supplied by a 230 V, 50 Hz source. The active power P and th...
Under worst case,
Pmax = 2 kW
Qmax = 2 kVAR
cos 45 = 0.707lag
View all questions of this test
Most Upvoted Answer
A load is supplied by a 230 V, 50 Hz source. The active power P and th...
Given Information:
- Supply voltage (V) = 230 V
- Frequency (f) = 50 Hz
- Active power (P) = 1 kW to 2 kW
- Reactive power (Q) = 1 kVAR
- Capacitor generates 1 kVAR reactive power for power factor correction.

Calculating Power Factor (PF) without Correction:
The power factor (PF) is the ratio of active power to apparent power. Apparent power (S) can be calculated using the following formula:

S = √(P^2 + Q^2)

Given that P = 1 kW and Q = 1 kVAR, we can calculate S:

S = √(1^2 + 1^2) = √2 kVA

The power factor (PF) can be calculated as:

PF = P / S = 1 / √2 ≈ 0.707 lagging

Calculating Power Factor (PF) with Correction:
To correct the power factor, a capacitor is connected across the load. The capacitor generates 1 kVAR reactive power.

The new reactive power (Q') after power factor correction can be calculated as:

Q' = Q - Capacitor Reactive Power

Q' = 1 kVAR - 1 kVAR = 0 kVAR

The new apparent power (S') can be calculated using the formula:

S' = √(P^2 + Q'^2) = √(1^2 + 0^2) = 1 kVA

The new power factor (PF') after power factor correction can be calculated as:

PF' = P / S' = 1 / 1 = 1 (unity power factor)

Worst Case Power Factor:
The worst case power factor after power factor correction occurs when the load is purely resistive (Q' = 0 kVAR). In this case, the power factor is 1 (unity power factor).

Therefore, the correct option is d) 1.
Explore Courses for Electrical Engineering (EE) exam

Similar Electrical Engineering (EE) Doubts

Top Courses for Electrical Engineering (EE)

A load is supplied by a 230 V, 50 Hz source. The active power P and the reactive power Q consumed by the load are such that 1 kW ≤P ≤2kW and 1 kVAR ≤Q ≤kVAR . A capacitor connected across the load for power factor correction generates 1 kVAR reactive power. The worst case power factor after power factor correction isa)0.447 lagb)0.707 lagc)0.894 lagd)1Correct answer is option 'B'. Can you explain this answer?
Question Description
A load is supplied by a 230 V, 50 Hz source. The active power P and the reactive power Q consumed by the load are such that 1 kW ≤P ≤2kW and 1 kVAR ≤Q ≤kVAR . A capacitor connected across the load for power factor correction generates 1 kVAR reactive power. The worst case power factor after power factor correction isa)0.447 lagb)0.707 lagc)0.894 lagd)1Correct answer is option 'B'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A load is supplied by a 230 V, 50 Hz source. The active power P and the reactive power Q consumed by the load are such that 1 kW ≤P ≤2kW and 1 kVAR ≤Q ≤kVAR . A capacitor connected across the load for power factor correction generates 1 kVAR reactive power. The worst case power factor after power factor correction isa)0.447 lagb)0.707 lagc)0.894 lagd)1Correct answer is option 'B'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A load is supplied by a 230 V, 50 Hz source. The active power P and the reactive power Q consumed by the load are such that 1 kW ≤P ≤2kW and 1 kVAR ≤Q ≤kVAR . A capacitor connected across the load for power factor correction generates 1 kVAR reactive power. The worst case power factor after power factor correction isa)0.447 lagb)0.707 lagc)0.894 lagd)1Correct answer is option 'B'. Can you explain this answer?.
Solutions for A load is supplied by a 230 V, 50 Hz source. The active power P and the reactive power Q consumed by the load are such that 1 kW ≤P ≤2kW and 1 kVAR ≤Q ≤kVAR . A capacitor connected across the load for power factor correction generates 1 kVAR reactive power. The worst case power factor after power factor correction isa)0.447 lagb)0.707 lagc)0.894 lagd)1Correct answer is option 'B'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of A load is supplied by a 230 V, 50 Hz source. The active power P and the reactive power Q consumed by the load are such that 1 kW ≤P ≤2kW and 1 kVAR ≤Q ≤kVAR . A capacitor connected across the load for power factor correction generates 1 kVAR reactive power. The worst case power factor after power factor correction isa)0.447 lagb)0.707 lagc)0.894 lagd)1Correct answer is option 'B'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A load is supplied by a 230 V, 50 Hz source. The active power P and the reactive power Q consumed by the load are such that 1 kW ≤P ≤2kW and 1 kVAR ≤Q ≤kVAR . A capacitor connected across the load for power factor correction generates 1 kVAR reactive power. The worst case power factor after power factor correction isa)0.447 lagb)0.707 lagc)0.894 lagd)1Correct answer is option 'B'. Can you explain this answer?, a detailed solution for A load is supplied by a 230 V, 50 Hz source. The active power P and the reactive power Q consumed by the load are such that 1 kW ≤P ≤2kW and 1 kVAR ≤Q ≤kVAR . A capacitor connected across the load for power factor correction generates 1 kVAR reactive power. The worst case power factor after power factor correction isa)0.447 lagb)0.707 lagc)0.894 lagd)1Correct answer is option 'B'. Can you explain this answer? has been provided alongside types of A load is supplied by a 230 V, 50 Hz source. The active power P and the reactive power Q consumed by the load are such that 1 kW ≤P ≤2kW and 1 kVAR ≤Q ≤kVAR . A capacitor connected across the load for power factor correction generates 1 kVAR reactive power. The worst case power factor after power factor correction isa)0.447 lagb)0.707 lagc)0.894 lagd)1Correct answer is option 'B'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A load is supplied by a 230 V, 50 Hz source. The active power P and the reactive power Q consumed by the load are such that 1 kW ≤P ≤2kW and 1 kVAR ≤Q ≤kVAR . A capacitor connected across the load for power factor correction generates 1 kVAR reactive power. The worst case power factor after power factor correction isa)0.447 lagb)0.707 lagc)0.894 lagd)1Correct answer is option 'B'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev