A 3 phase induction motor draws 1000 KVA at a p.f of 0.8 lag. A synchronous motor is connected in parallel to draw an additional 750 KVA at a power factor of 0.6 lead. The p.f of the total load supplied by the mains is . A. Unity B. 0707lead C. 0.6 lag D. Zero?
Most Upvoted Answer
A 3 phase induction motor draws 1000 KVA at a p.f of 0.8 lag. A synchr...
Solution:

Given data:

Induction motor power = 1000 KVA

Induction motor p.f = 0.8 lagging

Synchronous motor power = 750 KVA

Synchronous motor p.f = 0.6 leading

Total power = 1000 + 750 = 1750 KVA

Calculations:

Let's calculate the reactive power of both motors.

Reactive power of induction motor = √(1 - 0.8²) × 1000 = 600 KVAR (lagging)

Reactive power of synchronous motor = √(1 - 0.6²) × 750 = 600 KVAR (leading)

Total reactive power = 600 - 600 = 0 KVAR

Total apparent power = 1750 KVA

Total real power = 1750 × p.f = 1750 × 0.73 (average p.f) = 1277.5 KW

Total p.f = 1277.5 / 1750 = 0.73 lagging

Answer:

The p.f of the total load supplied by the mains is 0.73 lagging.

Explanation:

The given question is based on the concept of power factor correction using synchronous motors. The induction motor has a power factor of 0.8 lagging, which means it requires reactive power to operate. To improve the power factor, a synchronous motor is connected in parallel, which has a power factor of 0.6 leading. The synchronous motor supplies the reactive power required by the induction motor and improves the overall power factor of the system. The total power factor is calculated by finding the average power factor of the two motors. The final power factor obtained is 0.73 lagging, which is an improvement over the power factor of the induction motor.
Community Answer
A 3 phase induction motor draws 1000 KVA at a p.f of 0.8 lag. A synchr...
Correct answer is A .unity
but plz explain the solution
Explore Courses for Electrical Engineering (EE) exam

Similar Electrical Engineering (EE) Doubts

Top Courses for Electrical Engineering (EE)

A 3 phase induction motor draws 1000 KVA at a p.f of 0.8 lag. A synchronous motor is connected in parallel to draw an additional 750 KVA at a power factor of 0.6 lead. The p.f of the total load supplied by the mains is . A. Unity B. 0707lead C. 0.6 lag D. Zero?
Question Description
A 3 phase induction motor draws 1000 KVA at a p.f of 0.8 lag. A synchronous motor is connected in parallel to draw an additional 750 KVA at a power factor of 0.6 lead. The p.f of the total load supplied by the mains is . A. Unity B. 0707lead C. 0.6 lag D. Zero? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A 3 phase induction motor draws 1000 KVA at a p.f of 0.8 lag. A synchronous motor is connected in parallel to draw an additional 750 KVA at a power factor of 0.6 lead. The p.f of the total load supplied by the mains is . A. Unity B. 0707lead C. 0.6 lag D. Zero? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A 3 phase induction motor draws 1000 KVA at a p.f of 0.8 lag. A synchronous motor is connected in parallel to draw an additional 750 KVA at a power factor of 0.6 lead. The p.f of the total load supplied by the mains is . A. Unity B. 0707lead C. 0.6 lag D. Zero?.
Solutions for A 3 phase induction motor draws 1000 KVA at a p.f of 0.8 lag. A synchronous motor is connected in parallel to draw an additional 750 KVA at a power factor of 0.6 lead. The p.f of the total load supplied by the mains is . A. Unity B. 0707lead C. 0.6 lag D. Zero? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of A 3 phase induction motor draws 1000 KVA at a p.f of 0.8 lag. A synchronous motor is connected in parallel to draw an additional 750 KVA at a power factor of 0.6 lead. The p.f of the total load supplied by the mains is . A. Unity B. 0707lead C. 0.6 lag D. Zero? defined & explained in the simplest way possible. Besides giving the explanation of A 3 phase induction motor draws 1000 KVA at a p.f of 0.8 lag. A synchronous motor is connected in parallel to draw an additional 750 KVA at a power factor of 0.6 lead. The p.f of the total load supplied by the mains is . A. Unity B. 0707lead C. 0.6 lag D. Zero?, a detailed solution for A 3 phase induction motor draws 1000 KVA at a p.f of 0.8 lag. A synchronous motor is connected in parallel to draw an additional 750 KVA at a power factor of 0.6 lead. The p.f of the total load supplied by the mains is . A. Unity B. 0707lead C. 0.6 lag D. Zero? has been provided alongside types of A 3 phase induction motor draws 1000 KVA at a p.f of 0.8 lag. A synchronous motor is connected in parallel to draw an additional 750 KVA at a power factor of 0.6 lead. The p.f of the total load supplied by the mains is . A. Unity B. 0707lead C. 0.6 lag D. Zero? theory, EduRev gives you an ample number of questions to practice A 3 phase induction motor draws 1000 KVA at a p.f of 0.8 lag. A synchronous motor is connected in parallel to draw an additional 750 KVA at a power factor of 0.6 lead. The p.f of the total load supplied by the mains is . A. Unity B. 0707lead C. 0.6 lag D. Zero? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev