A counter flow double pipe heat exchanger is to heat water from 20oC to 80oC at a rate of 1.2kg/s. The heating is to be accomplished by geo-thermal water available at 160oC at a mass flow rate of 2 kg/s. The inner tube is thin-walled and has a diameter of 1.5 cm. The overall heat transfer coefficient of the heat exchanger is 620 W/m2-K . Determine the length of the heat exchanger required to achieve the desired heating. Given
NTU = specific heat of water is 4.18 Kj/kg-K and for geothermal water is 4.31 Kj/kg-K.
(B)110.0
    Correct answer is between ','. Can you explain this answer?
    Verified Answer
    A counter flow double pipe heat exchanger is to heat water from 20oC ...
    The capacity rates are,
    Ch = mhcph = 2 x 4.31 = 8.62 W/K
    Ch = mhcph = 1.2 x 4018 = 5.02 kW/K
    ∴ C = Cmin/Cmax = 5.02/8.62 = 0.582
    ∴ Qact = mccpc [Tce - Tci]
    = 1.2 x 4.18(80-20)
    = 301 kW
    Qmax = Cmin (Thi - Tci)
    = 5.02(160 - 20)
    = 702.8 kW
    ∴ ε Qact/Qmax = 301/702.8 = 0.428
    ⇒ NTU = 0.651
    ⇒ UA/Cmin = 0.651
    ⇒ A = 5.11 m2
    Now A = πDL
    ⇒ L = A/πD = 5.11/3.14 x 0.015
    ⇒ L = 108 m
    View all questions of this test
    Most Upvoted Answer
    A counter flow double pipe heat exchanger is to heat water from 20oC ...
    The capacity rates are,
    Ch = mhcph = 2 x 4.31 = 8.62 W/K
    Ch = mhcph = 1.2 x 4018 = 5.02 kW/K
    ∴ C = Cmin/Cmax = 5.02/8.62 = 0.582
    ∴ Qact = mccpc [Tce - Tci]
    = 1.2 x 4.18(80-20)
    = 301 kW
    Qmax = Cmin (Thi - Tci)
    = 5.02(160 - 20)
    = 702.8 kW
    ∴ ε Qact/Qmax = 301/702.8 = 0.428
    ⇒ NTU = 0.651
    ⇒ UA/Cmin = 0.651
    ⇒ A = 5.11 m2
    Now A = πDL
    ⇒ L = A/πD = 5.11/3.14 x 0.015
    ⇒ L = 108 m
    Free Test
    Community Answer
    A counter flow double pipe heat exchanger is to heat water from 20oC ...
    The capacity rates are,
    Ch = mhcph = 2 x 4.31 = 8.62 W/K
    Ch = mhcph = 1.2 x 4018 = 5.02 kW/K
    ∴ C = Cmin/Cmax = 5.02/8.62 = 0.582
    ∴ Qact = mccpc [Tce - Tci]
    = 1.2 x 4.18(80-20)
    = 301 kW
    Qmax = Cmin (Thi - Tci)
    = 5.02(160 - 20)
    = 702.8 kW
    ∴ ε Qact/Qmax = 301/702.8 = 0.428
    ⇒ NTU = 0.651
    ⇒ UA/Cmin = 0.651
    ⇒ A = 5.11 m2
    Now A = πDL
    ⇒ L = A/πD = 5.11/3.14 x 0.015
    ⇒ L = 108 m
    Explore Courses for Chemical Engineering exam

    Similar Chemical Engineering Doubts

    A counter flow double pipe heat exchanger is to heat water from 20oC to 80oC at a rate of 1.2kg/s. The heating is to be accomplished by geo-thermal water available at 160oC at a mass flow rate of 2 kg/s. The inner tube is thin-walled and has a diameter of 1.5 cm. The overall heat transfer coefficient of the heat exchanger is 620 W/m2-K . Determine the length of the heat exchanger required to achieve the desired heating. GivenNTU = specific heat of water is 4.18 Kj/kg-K and for geothermal water is 4.31 Kj/kg-K.(B)110.0Correct answer is between ','. Can you explain this answer?
    Question Description
    A counter flow double pipe heat exchanger is to heat water from 20oC to 80oC at a rate of 1.2kg/s. The heating is to be accomplished by geo-thermal water available at 160oC at a mass flow rate of 2 kg/s. The inner tube is thin-walled and has a diameter of 1.5 cm. The overall heat transfer coefficient of the heat exchanger is 620 W/m2-K . Determine the length of the heat exchanger required to achieve the desired heating. GivenNTU = specific heat of water is 4.18 Kj/kg-K and for geothermal water is 4.31 Kj/kg-K.(B)110.0Correct answer is between ','. Can you explain this answer? for Chemical Engineering 2024 is part of Chemical Engineering preparation. The Question and answers have been prepared according to the Chemical Engineering exam syllabus. Information about A counter flow double pipe heat exchanger is to heat water from 20oC to 80oC at a rate of 1.2kg/s. The heating is to be accomplished by geo-thermal water available at 160oC at a mass flow rate of 2 kg/s. The inner tube is thin-walled and has a diameter of 1.5 cm. The overall heat transfer coefficient of the heat exchanger is 620 W/m2-K . Determine the length of the heat exchanger required to achieve the desired heating. GivenNTU = specific heat of water is 4.18 Kj/kg-K and for geothermal water is 4.31 Kj/kg-K.(B)110.0Correct answer is between ','. Can you explain this answer? covers all topics & solutions for Chemical Engineering 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A counter flow double pipe heat exchanger is to heat water from 20oC to 80oC at a rate of 1.2kg/s. The heating is to be accomplished by geo-thermal water available at 160oC at a mass flow rate of 2 kg/s. The inner tube is thin-walled and has a diameter of 1.5 cm. The overall heat transfer coefficient of the heat exchanger is 620 W/m2-K . Determine the length of the heat exchanger required to achieve the desired heating. GivenNTU = specific heat of water is 4.18 Kj/kg-K and for geothermal water is 4.31 Kj/kg-K.(B)110.0Correct answer is between ','. Can you explain this answer?.
    Solutions for A counter flow double pipe heat exchanger is to heat water from 20oC to 80oC at a rate of 1.2kg/s. The heating is to be accomplished by geo-thermal water available at 160oC at a mass flow rate of 2 kg/s. The inner tube is thin-walled and has a diameter of 1.5 cm. The overall heat transfer coefficient of the heat exchanger is 620 W/m2-K . Determine the length of the heat exchanger required to achieve the desired heating. GivenNTU = specific heat of water is 4.18 Kj/kg-K and for geothermal water is 4.31 Kj/kg-K.(B)110.0Correct answer is between ','. Can you explain this answer? in English & in Hindi are available as part of our courses for Chemical Engineering. Download more important topics, notes, lectures and mock test series for Chemical Engineering Exam by signing up for free.
    Here you can find the meaning of A counter flow double pipe heat exchanger is to heat water from 20oC to 80oC at a rate of 1.2kg/s. The heating is to be accomplished by geo-thermal water available at 160oC at a mass flow rate of 2 kg/s. The inner tube is thin-walled and has a diameter of 1.5 cm. The overall heat transfer coefficient of the heat exchanger is 620 W/m2-K . Determine the length of the heat exchanger required to achieve the desired heating. GivenNTU = specific heat of water is 4.18 Kj/kg-K and for geothermal water is 4.31 Kj/kg-K.(B)110.0Correct answer is between ','. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A counter flow double pipe heat exchanger is to heat water from 20oC to 80oC at a rate of 1.2kg/s. The heating is to be accomplished by geo-thermal water available at 160oC at a mass flow rate of 2 kg/s. The inner tube is thin-walled and has a diameter of 1.5 cm. The overall heat transfer coefficient of the heat exchanger is 620 W/m2-K . Determine the length of the heat exchanger required to achieve the desired heating. GivenNTU = specific heat of water is 4.18 Kj/kg-K and for geothermal water is 4.31 Kj/kg-K.(B)110.0Correct answer is between ','. Can you explain this answer?, a detailed solution for A counter flow double pipe heat exchanger is to heat water from 20oC to 80oC at a rate of 1.2kg/s. The heating is to be accomplished by geo-thermal water available at 160oC at a mass flow rate of 2 kg/s. The inner tube is thin-walled and has a diameter of 1.5 cm. The overall heat transfer coefficient of the heat exchanger is 620 W/m2-K . Determine the length of the heat exchanger required to achieve the desired heating. GivenNTU = specific heat of water is 4.18 Kj/kg-K and for geothermal water is 4.31 Kj/kg-K.(B)110.0Correct answer is between ','. Can you explain this answer? has been provided alongside types of A counter flow double pipe heat exchanger is to heat water from 20oC to 80oC at a rate of 1.2kg/s. The heating is to be accomplished by geo-thermal water available at 160oC at a mass flow rate of 2 kg/s. The inner tube is thin-walled and has a diameter of 1.5 cm. The overall heat transfer coefficient of the heat exchanger is 620 W/m2-K . Determine the length of the heat exchanger required to achieve the desired heating. GivenNTU = specific heat of water is 4.18 Kj/kg-K and for geothermal water is 4.31 Kj/kg-K.(B)110.0Correct answer is between ','. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A counter flow double pipe heat exchanger is to heat water from 20oC to 80oC at a rate of 1.2kg/s. The heating is to be accomplished by geo-thermal water available at 160oC at a mass flow rate of 2 kg/s. The inner tube is thin-walled and has a diameter of 1.5 cm. The overall heat transfer coefficient of the heat exchanger is 620 W/m2-K . Determine the length of the heat exchanger required to achieve the desired heating. GivenNTU = specific heat of water is 4.18 Kj/kg-K and for geothermal water is 4.31 Kj/kg-K.(B)110.0Correct answer is between ','. Can you explain this answer? tests, examples and also practice Chemical Engineering tests.
    Explore Courses for Chemical Engineering exam
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev