Electrical Engineering (EE) Exam  >  Electrical Engineering (EE) Questions  >   A 4 pole, Y-connected salient pole 440 V, 50... Start Learning for Free
A 4 pole, Y-connected salient pole 440 V, 50 Hz synchronous motor draw 18 kVA at 0.8 p.f. lag from supply. The motor has xd = 4.5Ω and xq = 3Ωwhile armature resistance is negligible. But due to improper connection the field conductor opens and field current falls to zero. The mechanical output torque of motor will be _____ N-m. (rounded off to two decimal places)
    Correct answer is '34.24'. Can you explain this answer?
    Most Upvoted Answer
    A 4 pole, Y-connected salient pole 440 V, 50 Hz synchronous motor dra...
    Given: p=4
    xq = 3Ω
    Ra = 0
    For a salient pole machine at lag p.f.
    ∴Φ-δ = 21.87o and δ = 15o
    Due to field opens, the field current falls to zero. In salient pole motor even if field current falls to zero (i.e. excitation becomes zero), the motor continues to run as reluctance motor at synchronous speed.
    At such condition,
    and output mechanical torque =
    Free Test
    Community Answer
    A 4 pole, Y-connected salient pole 440 V, 50 Hz synchronous motor dra...
    Given information:
    - Synchronous motor: 4 pole, Y-connected salient pole
    - Rated voltage: 440 V
    - Rated frequency: 50 Hz
    - Rated apparent power: 18 kVA
    - Power factor: 0.8 lagging
    - Synchronous reactance (Xd): 4.5 Ω
    - Synchronous reactance (Xq): 3 Ω
    - Armature resistance: negligible

    Step 1: Calculating the synchronous speed
    The synchronous speed of a synchronous motor is given by the formula:
    Ns = 120f / P
    Where,
    Ns = synchronous speed in RPM
    f = frequency in Hz
    P = number of poles

    Substituting the given values:
    Ns = 120 * 50 / 4 = 1500 RPM

    Step 2: Calculating the synchronous impedance
    The synchronous impedance (Zs) of a synchronous motor is given by the formula:
    Zs = √(Rs^2 + (Xs - Xm)^2)
    Where,
    Rs = armature resistance
    Xs = synchronous reactance
    Xm = magnetizing reactance

    Since the armature resistance is negligible, the synchronous impedance simplifies to:
    Zs = √(Xs^2 + Xm^2)

    Substituting the given values:
    Zs = √(4.5^2 + 3^2) = √(20.25 + 9) = √29.25 ≈ 5.41 Ω

    Step 3: Calculating the synchronous current
    The synchronous current (Is) can be calculated using the formula:
    Is = V / Zs
    Where,
    V = rated voltage

    Substituting the given value:
    Is = 440 / 5.41 ≈ 81.26 A

    Step 4: Calculating the power angle
    The power angle (δ) can be calculated using the formula:
    δ = cos^(-1)(p.f)

    Substituting the given power factor:
    δ = cos^(-1)(0.8) ≈ 36.87°

    Step 5: Calculating the field current
    Due to the improper connection, the field conductor opens and the field current becomes zero.

    Step 6: Calculating the mechanical torque
    The mechanical torque (Tm) can be calculated using the formula:
    Tm = (3 * V^2 * p.f) / (2 * π * f * Is * sin(δ))
    Where,
    V = rated voltage
    p.f = power factor
    f = frequency
    Is = synchronous current
    δ = power angle

    Substituting the given values:
    Tm = (3 * 440^2 * 0.8) / (2 * π * 50 * 81.26 * sin(36.87°))
    ≈ 34.24 N-m

    Therefore, the mechanical output torque of the motor will be approximately 34.24 N-m.
    Explore Courses for Electrical Engineering (EE) exam

    Similar Electrical Engineering (EE) Doubts

    Top Courses for Electrical Engineering (EE)

    A 4 pole, Y-connected salient pole 440 V, 50 Hz synchronous motor draw 18 kVA at 0.8 p.f. lag from supply. The motor has xd = 4.5Ω and xq = 3Ωwhile armature resistance is negligible. But due to improper connection the field conductor opens and field current falls to zero. The mechanical output torque of motor will be _____ N-m. (rounded off to two decimal places)Correct answer is '34.24'. Can you explain this answer?
    Question Description
    A 4 pole, Y-connected salient pole 440 V, 50 Hz synchronous motor draw 18 kVA at 0.8 p.f. lag from supply. The motor has xd = 4.5Ω and xq = 3Ωwhile armature resistance is negligible. But due to improper connection the field conductor opens and field current falls to zero. The mechanical output torque of motor will be _____ N-m. (rounded off to two decimal places)Correct answer is '34.24'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A 4 pole, Y-connected salient pole 440 V, 50 Hz synchronous motor draw 18 kVA at 0.8 p.f. lag from supply. The motor has xd = 4.5Ω and xq = 3Ωwhile armature resistance is negligible. But due to improper connection the field conductor opens and field current falls to zero. The mechanical output torque of motor will be _____ N-m. (rounded off to two decimal places)Correct answer is '34.24'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A 4 pole, Y-connected salient pole 440 V, 50 Hz synchronous motor draw 18 kVA at 0.8 p.f. lag from supply. The motor has xd = 4.5Ω and xq = 3Ωwhile armature resistance is negligible. But due to improper connection the field conductor opens and field current falls to zero. The mechanical output torque of motor will be _____ N-m. (rounded off to two decimal places)Correct answer is '34.24'. Can you explain this answer?.
    Solutions for A 4 pole, Y-connected salient pole 440 V, 50 Hz synchronous motor draw 18 kVA at 0.8 p.f. lag from supply. The motor has xd = 4.5Ω and xq = 3Ωwhile armature resistance is negligible. But due to improper connection the field conductor opens and field current falls to zero. The mechanical output torque of motor will be _____ N-m. (rounded off to two decimal places)Correct answer is '34.24'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
    Here you can find the meaning of A 4 pole, Y-connected salient pole 440 V, 50 Hz synchronous motor draw 18 kVA at 0.8 p.f. lag from supply. The motor has xd = 4.5Ω and xq = 3Ωwhile armature resistance is negligible. But due to improper connection the field conductor opens and field current falls to zero. The mechanical output torque of motor will be _____ N-m. (rounded off to two decimal places)Correct answer is '34.24'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A 4 pole, Y-connected salient pole 440 V, 50 Hz synchronous motor draw 18 kVA at 0.8 p.f. lag from supply. The motor has xd = 4.5Ω and xq = 3Ωwhile armature resistance is negligible. But due to improper connection the field conductor opens and field current falls to zero. The mechanical output torque of motor will be _____ N-m. (rounded off to two decimal places)Correct answer is '34.24'. Can you explain this answer?, a detailed solution for A 4 pole, Y-connected salient pole 440 V, 50 Hz synchronous motor draw 18 kVA at 0.8 p.f. lag from supply. The motor has xd = 4.5Ω and xq = 3Ωwhile armature resistance is negligible. But due to improper connection the field conductor opens and field current falls to zero. The mechanical output torque of motor will be _____ N-m. (rounded off to two decimal places)Correct answer is '34.24'. Can you explain this answer? has been provided alongside types of A 4 pole, Y-connected salient pole 440 V, 50 Hz synchronous motor draw 18 kVA at 0.8 p.f. lag from supply. The motor has xd = 4.5Ω and xq = 3Ωwhile armature resistance is negligible. But due to improper connection the field conductor opens and field current falls to zero. The mechanical output torque of motor will be _____ N-m. (rounded off to two decimal places)Correct answer is '34.24'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A 4 pole, Y-connected salient pole 440 V, 50 Hz synchronous motor draw 18 kVA at 0.8 p.f. lag from supply. The motor has xd = 4.5Ω and xq = 3Ωwhile armature resistance is negligible. But due to improper connection the field conductor opens and field current falls to zero. The mechanical output torque of motor will be _____ N-m. (rounded off to two decimal places)Correct answer is '34.24'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Explore Courses
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev