A 2300 V three phase star connected synchronous motor has armature
resistance of 0.2 ohm/ph. and synchronous reactance of 2.2 ohm/ph.
The motor is operated at 0.5 leading power factor and takes a current
of 200 A from supply. Calculate back EMF generated in the motor &
load angle.?
Most Upvoted Answer
A 2300 V three phase star connected synchronous motor has armature res...
Given Data
- Line Voltage (V) = 2300 V
- Armature Resistance (Ra) = 0.2 ohm/ph
- Synchronous Reactance (Xs) = 2.2 ohm/ph
- Current (I) = 200 A
- Power Factor = 0.5 (Leading)
Calculating Phase Voltage
- Phase Voltage (Vph) = V / √3 = 2300 / √3 ≈ 1325.9 V
Calculating Armature Current in Each Phase
- Iph = I = 200 A (since it is star-connected)
Calculating Voltage Drop Across Armature Resistance
- Voltage Drop (V_Ra) = Iph * Ra = 200 * 0.2 = 40 V
Calculating Voltage Drop Across Synchronous Reactance
- Voltage Drop (V_Xs) = Iph * Xs = 200 * 2.2 = 440 V
Calculating Back EMF (E)
- Using the formula: E = Vph + V_Ra + V_Xs
- E = 1325.9 + 40 + 440 = 1805.9 V
Calculating Load Angle (δ)
- Power Factor Angle (φ) = cos⁻¹(0.5) = 60 degrees
- Load Angle (δ) = φ = 60 degrees
Results
- Back EMF (E): Approximately 1805.9 V
- Load Angle (δ): 60 degrees
This analysis provides insights into the synchronous motor's performance, indicating a significant back EMF with a leading power factor.
Explore Courses for UPSC exam

Similar UPSC Doubts

Top Courses for UPSC

A 2300 V three phase star connected synchronous motor has armature resistance of 0.2 ohm/ph. and synchronous reactance of 2.2 ohm/ph. The motor is operated at 0.5 leading power factor and takes a current of 200 A from supply. Calculate back EMF generated in the motor & load angle.?
Question Description
A 2300 V three phase star connected synchronous motor has armature resistance of 0.2 ohm/ph. and synchronous reactance of 2.2 ohm/ph. The motor is operated at 0.5 leading power factor and takes a current of 200 A from supply. Calculate back EMF generated in the motor & load angle.? for UPSC 2024 is part of UPSC preparation. The Question and answers have been prepared according to the UPSC exam syllabus. Information about A 2300 V three phase star connected synchronous motor has armature resistance of 0.2 ohm/ph. and synchronous reactance of 2.2 ohm/ph. The motor is operated at 0.5 leading power factor and takes a current of 200 A from supply. Calculate back EMF generated in the motor & load angle.? covers all topics & solutions for UPSC 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A 2300 V three phase star connected synchronous motor has armature resistance of 0.2 ohm/ph. and synchronous reactance of 2.2 ohm/ph. The motor is operated at 0.5 leading power factor and takes a current of 200 A from supply. Calculate back EMF generated in the motor & load angle.?.
Solutions for A 2300 V three phase star connected synchronous motor has armature resistance of 0.2 ohm/ph. and synchronous reactance of 2.2 ohm/ph. The motor is operated at 0.5 leading power factor and takes a current of 200 A from supply. Calculate back EMF generated in the motor & load angle.? in English & in Hindi are available as part of our courses for UPSC. Download more important topics, notes, lectures and mock test series for UPSC Exam by signing up for free.
Here you can find the meaning of A 2300 V three phase star connected synchronous motor has armature resistance of 0.2 ohm/ph. and synchronous reactance of 2.2 ohm/ph. The motor is operated at 0.5 leading power factor and takes a current of 200 A from supply. Calculate back EMF generated in the motor & load angle.? defined & explained in the simplest way possible. Besides giving the explanation of A 2300 V three phase star connected synchronous motor has armature resistance of 0.2 ohm/ph. and synchronous reactance of 2.2 ohm/ph. The motor is operated at 0.5 leading power factor and takes a current of 200 A from supply. Calculate back EMF generated in the motor & load angle.?, a detailed solution for A 2300 V three phase star connected synchronous motor has armature resistance of 0.2 ohm/ph. and synchronous reactance of 2.2 ohm/ph. The motor is operated at 0.5 leading power factor and takes a current of 200 A from supply. Calculate back EMF generated in the motor & load angle.? has been provided alongside types of A 2300 V three phase star connected synchronous motor has armature resistance of 0.2 ohm/ph. and synchronous reactance of 2.2 ohm/ph. The motor is operated at 0.5 leading power factor and takes a current of 200 A from supply. Calculate back EMF generated in the motor & load angle.? theory, EduRev gives you an ample number of questions to practice A 2300 V three phase star connected synchronous motor has armature resistance of 0.2 ohm/ph. and synchronous reactance of 2.2 ohm/ph. The motor is operated at 0.5 leading power factor and takes a current of 200 A from supply. Calculate back EMF generated in the motor & load angle.? tests, examples and also practice UPSC tests.
Explore Courses for UPSC exam

Top Courses for UPSC

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev