water(Cp=4180J/kgoC)enter into the 2.5 cm internal diameter tube of a double pipe counter flow heat exchanger at 17oC at a rate of 3kg/s .Water is heated by steam condensing at 120oC (hfg= 2203kj/kg)in the shell .If overall heat transfer coefficient of the heat exchanger is 900W/m2oC ,determine the length of the tube required in order to heat the water to 80oC using LMTD n NTU method?
Most Upvoted Answer
water(Cp=4180J/kgoC)enter into the 2.5 cm internal diameter tube of a ...
Problem:

Water (Cp=4180J/kgoC) enters into the 2.5 cm internal diameter tube of a double pipe counter flow heat exchanger at 17oC at a rate of 3kg/s. Water is heated by steam condensing at 120oC (hfg= 2203kj/kg) in the shell. If the overall heat transfer coefficient of the heat exchanger is 900W/m2oC, determine the length of the tube required in order to heat the water to 80oC using LMTD and NTU method?


Solution:

Step 1: Determine the LMTD

LMTD (Logarithmic Mean Temperature Difference) is determined using the formula:

LMTD = (ΔT1 - ΔT2) / ln(ΔT1 / ΔT2)

where ΔT1 = T1,in - T2,out and ΔT2 = T1,out - T2,in

Given:


  • T1,in = 17oC

  • T1,out = 80oC

  • T2,in = 120oC

  • T2,out = ? (unknown)


Using the formula to calculate ΔT1 and ΔT2:


  • ΔT1 = 17 - T2,out

  • ΔT2 = 120 - 80 = 40


Substituting the values in the LMTD formula:

LMTD = (17 - T2,out - 40) / ln((17 - T2,out) / 40)

LMTD = (57 - T2,out) / ln((17 - T2,out) / 40)


Step 2: Determine the NTU

NTU (Number of Transfer Units) is determined using the formula:

NTU = UA / Cp_min

where U is the overall heat transfer coefficient, A is the heat transfer area, and Cp_min is the minimum heat capacity.

Given:


  • U = 900 W/m2oC

  • A = πDL (where D is the inner diameter of the tube and L is the length of the tube)

  • Cp_min = 4180 J/kgoC (for water)


Substituting the values in the NTU formula:

NTU = (900 x π x 0.025 x L) / 4180

NTU = 0.017 x L


Step 3: Determine the Effectiveness

Effectiveness is determined using the formula:

ε = (1 - e^(-NTU(1 - C))) / (1 - C x e^(-NTU(1 - C)))

where C = (Cp_min,C / Cp_max,F) and Cp_max,F is the
Community Answer
water(Cp=4180J/kgoC)enter into the 2.5 cm internal diameter tube of a ...
Water (Cp = 4180 J/kg � �C) enters the 2.5-cm internaldiameter tube of a double-pipe counter-flow heat exchanger at 17�C at a rate of3 kg/s. It is heated by steam condensing at 120�C (hfg = 2203 kJ/kg) in theshell. If the overall heat transfer coefficient of the heat exchanger is 1500W/m2 �C, determine the length of the tube required in order to heatthe water to 80�C.
Explore Courses for GATE exam
water(Cp=4180J/kgoC)enter into the 2.5 cm internal diameter tube of a double pipe counter flow heat exchanger at 17oC at a rate of 3kg/s .Water is heated by steam condensing at 120oC (hfg= 2203kj/kg)in the shell .If overall heat transfer coefficient of the heat exchanger is 900W/m2oC ,determine the length of the tube required in order to heat the water to 80oC using LMTD n NTU method?
Question Description
water(Cp=4180J/kgoC)enter into the 2.5 cm internal diameter tube of a double pipe counter flow heat exchanger at 17oC at a rate of 3kg/s .Water is heated by steam condensing at 120oC (hfg= 2203kj/kg)in the shell .If overall heat transfer coefficient of the heat exchanger is 900W/m2oC ,determine the length of the tube required in order to heat the water to 80oC using LMTD n NTU method? for GATE 2024 is part of GATE preparation. The Question and answers have been prepared according to the GATE exam syllabus. Information about water(Cp=4180J/kgoC)enter into the 2.5 cm internal diameter tube of a double pipe counter flow heat exchanger at 17oC at a rate of 3kg/s .Water is heated by steam condensing at 120oC (hfg= 2203kj/kg)in the shell .If overall heat transfer coefficient of the heat exchanger is 900W/m2oC ,determine the length of the tube required in order to heat the water to 80oC using LMTD n NTU method? covers all topics & solutions for GATE 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for water(Cp=4180J/kgoC)enter into the 2.5 cm internal diameter tube of a double pipe counter flow heat exchanger at 17oC at a rate of 3kg/s .Water is heated by steam condensing at 120oC (hfg= 2203kj/kg)in the shell .If overall heat transfer coefficient of the heat exchanger is 900W/m2oC ,determine the length of the tube required in order to heat the water to 80oC using LMTD n NTU method?.
Solutions for water(Cp=4180J/kgoC)enter into the 2.5 cm internal diameter tube of a double pipe counter flow heat exchanger at 17oC at a rate of 3kg/s .Water is heated by steam condensing at 120oC (hfg= 2203kj/kg)in the shell .If overall heat transfer coefficient of the heat exchanger is 900W/m2oC ,determine the length of the tube required in order to heat the water to 80oC using LMTD n NTU method? in English & in Hindi are available as part of our courses for GATE. Download more important topics, notes, lectures and mock test series for GATE Exam by signing up for free.
Here you can find the meaning of water(Cp=4180J/kgoC)enter into the 2.5 cm internal diameter tube of a double pipe counter flow heat exchanger at 17oC at a rate of 3kg/s .Water is heated by steam condensing at 120oC (hfg= 2203kj/kg)in the shell .If overall heat transfer coefficient of the heat exchanger is 900W/m2oC ,determine the length of the tube required in order to heat the water to 80oC using LMTD n NTU method? defined & explained in the simplest way possible. Besides giving the explanation of water(Cp=4180J/kgoC)enter into the 2.5 cm internal diameter tube of a double pipe counter flow heat exchanger at 17oC at a rate of 3kg/s .Water is heated by steam condensing at 120oC (hfg= 2203kj/kg)in the shell .If overall heat transfer coefficient of the heat exchanger is 900W/m2oC ,determine the length of the tube required in order to heat the water to 80oC using LMTD n NTU method?, a detailed solution for water(Cp=4180J/kgoC)enter into the 2.5 cm internal diameter tube of a double pipe counter flow heat exchanger at 17oC at a rate of 3kg/s .Water is heated by steam condensing at 120oC (hfg= 2203kj/kg)in the shell .If overall heat transfer coefficient of the heat exchanger is 900W/m2oC ,determine the length of the tube required in order to heat the water to 80oC using LMTD n NTU method? has been provided alongside types of water(Cp=4180J/kgoC)enter into the 2.5 cm internal diameter tube of a double pipe counter flow heat exchanger at 17oC at a rate of 3kg/s .Water is heated by steam condensing at 120oC (hfg= 2203kj/kg)in the shell .If overall heat transfer coefficient of the heat exchanger is 900W/m2oC ,determine the length of the tube required in order to heat the water to 80oC using LMTD n NTU method? theory, EduRev gives you an ample number of questions to practice water(Cp=4180J/kgoC)enter into the 2.5 cm internal diameter tube of a double pipe counter flow heat exchanger at 17oC at a rate of 3kg/s .Water is heated by steam condensing at 120oC (hfg= 2203kj/kg)in the shell .If overall heat transfer coefficient of the heat exchanger is 900W/m2oC ,determine the length of the tube required in order to heat the water to 80oC using LMTD n NTU method? tests, examples and also practice GATE tests.
Explore Courses for GATE exam
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev