A parallelepiped enclosure measures 3 m × 3.5 m with 4 m height. The bottom floor having 0.75 emissivity is maintained at 380 K and all other surfaces (emissivity = 0.8) are maintained at 505 K. The net radiation (in kW) to the floor will be
    Correct answer is between '19,19.5'. Can you explain this answer?
    Verified Answer
    A parallelepiped enclosure measures 3 m × 3.5 m with 4 m height....
    As per the given data,
    A1 = area of four walls and ceiling

    View all questions of this test
    Explore Courses for GATE exam
    A parallelepiped enclosure measures 3 m × 3.5 m with 4 m height. The bottom floor having 0.75 emissivity is maintained at 380 K and all other surfaces (emissivity = 0.8) are maintained at 505 K. The net radiation (in kW) to the floor will beCorrect answer is between '19,19.5'. Can you explain this answer?
    Question Description
    A parallelepiped enclosure measures 3 m × 3.5 m with 4 m height. The bottom floor having 0.75 emissivity is maintained at 380 K and all other surfaces (emissivity = 0.8) are maintained at 505 K. The net radiation (in kW) to the floor will beCorrect answer is between '19,19.5'. Can you explain this answer? for GATE 2024 is part of GATE preparation. The Question and answers have been prepared according to the GATE exam syllabus. Information about A parallelepiped enclosure measures 3 m × 3.5 m with 4 m height. The bottom floor having 0.75 emissivity is maintained at 380 K and all other surfaces (emissivity = 0.8) are maintained at 505 K. The net radiation (in kW) to the floor will beCorrect answer is between '19,19.5'. Can you explain this answer? covers all topics & solutions for GATE 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A parallelepiped enclosure measures 3 m × 3.5 m with 4 m height. The bottom floor having 0.75 emissivity is maintained at 380 K and all other surfaces (emissivity = 0.8) are maintained at 505 K. The net radiation (in kW) to the floor will beCorrect answer is between '19,19.5'. Can you explain this answer?.
    Solutions for A parallelepiped enclosure measures 3 m × 3.5 m with 4 m height. The bottom floor having 0.75 emissivity is maintained at 380 K and all other surfaces (emissivity = 0.8) are maintained at 505 K. The net radiation (in kW) to the floor will beCorrect answer is between '19,19.5'. Can you explain this answer? in English & in Hindi are available as part of our courses for GATE. Download more important topics, notes, lectures and mock test series for GATE Exam by signing up for free.
    Here you can find the meaning of A parallelepiped enclosure measures 3 m × 3.5 m with 4 m height. The bottom floor having 0.75 emissivity is maintained at 380 K and all other surfaces (emissivity = 0.8) are maintained at 505 K. The net radiation (in kW) to the floor will beCorrect answer is between '19,19.5'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A parallelepiped enclosure measures 3 m × 3.5 m with 4 m height. The bottom floor having 0.75 emissivity is maintained at 380 K and all other surfaces (emissivity = 0.8) are maintained at 505 K. The net radiation (in kW) to the floor will beCorrect answer is between '19,19.5'. Can you explain this answer?, a detailed solution for A parallelepiped enclosure measures 3 m × 3.5 m with 4 m height. The bottom floor having 0.75 emissivity is maintained at 380 K and all other surfaces (emissivity = 0.8) are maintained at 505 K. The net radiation (in kW) to the floor will beCorrect answer is between '19,19.5'. Can you explain this answer? has been provided alongside types of A parallelepiped enclosure measures 3 m × 3.5 m with 4 m height. The bottom floor having 0.75 emissivity is maintained at 380 K and all other surfaces (emissivity = 0.8) are maintained at 505 K. The net radiation (in kW) to the floor will beCorrect answer is between '19,19.5'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A parallelepiped enclosure measures 3 m × 3.5 m with 4 m height. The bottom floor having 0.75 emissivity is maintained at 380 K and all other surfaces (emissivity = 0.8) are maintained at 505 K. The net radiation (in kW) to the floor will beCorrect answer is between '19,19.5'. Can you explain this answer? tests, examples and also practice GATE tests.
    Explore Courses for GATE exam
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev