GATE Exam  >  GATE Questions  >  While measuring power of a three-phase balanc... Start Learning for Free
While measuring power of a three-phase balanced load by the two-wattmeter method, the readings are 100W and 250 W. The power factor of the load is ______________.
    Correct answer is '0.802'. Can you explain this answer?
    Verified Answer
    While measuring power of a three-phase balanced load by the two-wattme...
    View all questions of this test
    Most Upvoted Answer
    While measuring power of a three-phase balanced load by the two-wattme...
    Given:
    - Readings of the two-wattmeter method: 100W and 250W

    To Find:
    - Power factor of the load

    Solution:
    The two-wattmeter method is used to measure the power of a three-phase balanced load. In this method, two wattmeters are connected to measure the power in each phase, and the sum of the readings gives the total power.

    Step 1: Calculating the Total Power
    The total power (P) can be calculated by adding the readings of the two wattmeters.
    P = P1 + P2
    P = 100W + 250W
    P = 350W

    Step 2: Calculating the Reactive Power
    The reactive power (Q) is given by:
    Q = √(P^2 - S^2)
    where P is the total power and S is the apparent power.
    In a balanced load, the apparent power is given by:
    S = √(P^2 + Q^2)
    Substituting the values:
    S = √(350^2 + Q^2)

    Step 3: Calculating the Power Factor
    The power factor (PF) is given by the ratio of the total power to the apparent power.
    PF = P/S
    PF = 350W / √(350^2 + Q^2)

    Step 4: Solving for the Power Factor
    To find the value of the power factor, we need to determine the value of Q.
    Since the load is balanced, the reactive power in each phase is equal. Therefore, Q can be calculated as:
    Q = √3 * |P1 - P2|
    Q = √3 * |100W - 250W|
    Q = √3 * |-150W|
    Q = √3 * 150W
    Q = 150√3 W

    Substituting the value of Q:
    PF = 350W / √(350^2 + (150√3)^2)
    PF = 350W / √(350^2 + 150^2 * 3)
    PF = 350W / √(122500 + 67500)
    PF = 350W / √190000
    PF = 350W / 435.89
    PF ≈ 0.802

    Therefore, the power factor of the load is approximately 0.802.
    Explore Courses for GATE exam
    While measuring power of a three-phase balanced load by the two-wattmeter method, the readings are 100W and 250 W. The power factor of the load is ______________.Correct answer is '0.802'. Can you explain this answer?
    Question Description
    While measuring power of a three-phase balanced load by the two-wattmeter method, the readings are 100W and 250 W. The power factor of the load is ______________.Correct answer is '0.802'. Can you explain this answer? for GATE 2024 is part of GATE preparation. The Question and answers have been prepared according to the GATE exam syllabus. Information about While measuring power of a three-phase balanced load by the two-wattmeter method, the readings are 100W and 250 W. The power factor of the load is ______________.Correct answer is '0.802'. Can you explain this answer? covers all topics & solutions for GATE 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for While measuring power of a three-phase balanced load by the two-wattmeter method, the readings are 100W and 250 W. The power factor of the load is ______________.Correct answer is '0.802'. Can you explain this answer?.
    Solutions for While measuring power of a three-phase balanced load by the two-wattmeter method, the readings are 100W and 250 W. The power factor of the load is ______________.Correct answer is '0.802'. Can you explain this answer? in English & in Hindi are available as part of our courses for GATE. Download more important topics, notes, lectures and mock test series for GATE Exam by signing up for free.
    Here you can find the meaning of While measuring power of a three-phase balanced load by the two-wattmeter method, the readings are 100W and 250 W. The power factor of the load is ______________.Correct answer is '0.802'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of While measuring power of a three-phase balanced load by the two-wattmeter method, the readings are 100W and 250 W. The power factor of the load is ______________.Correct answer is '0.802'. Can you explain this answer?, a detailed solution for While measuring power of a three-phase balanced load by the two-wattmeter method, the readings are 100W and 250 W. The power factor of the load is ______________.Correct answer is '0.802'. Can you explain this answer? has been provided alongside types of While measuring power of a three-phase balanced load by the two-wattmeter method, the readings are 100W and 250 W. The power factor of the load is ______________.Correct answer is '0.802'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice While measuring power of a three-phase balanced load by the two-wattmeter method, the readings are 100W and 250 W. The power factor of the load is ______________.Correct answer is '0.802'. Can you explain this answer? tests, examples and also practice GATE tests.
    Explore Courses for GATE exam
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev