A 500 MW, 21 kV, 50 Hz, 3-phase, 2-pole synchronous generator having a rated pf = 0.9, has a moment of inertia of 27.5 x 103 kg-m2. The inertia constant (H, in sec) will be _____. (Answer up to two decimal places)
Correct answer is '2.44'. Can you explain this answer?
Most Upvoted Answer
A 500 MW, 21 kV, 50 Hz, 3-phase, 2-pole synchronous generator having ...
Calculation of Inertia Constant of a Synchronous Generator

Given parameters:
• Power rating (P) = 500 MW
• Voltage rating (V) = 21 kV
• Frequency (f) = 50 Hz
• Number of phases (φ) = 3
• Number of poles (p) = 2
• Power factor (pf) = 0.9
• Moment of inertia (J) = 27.5 x 103 kg-m2

Formula for inertia constant (H):
H = J / (P × f × (1 - pf2) × p / φ)

Substituting the given values in the formula:
H = 27.5 x 103 / (500 x 106 × 50 × (1 - 0.92) × 2 / 3)
H = 2.44 seconds (rounded off to two decimal places)

Therefore, the inertia constant of the synchronous generator is 2.44 seconds.
Free Test
Community Answer
A 500 MW, 21 kV, 50 Hz, 3-phase, 2-pole synchronous generator having ...
Generator rating in MVA
= 2.44sec
Explore Courses for Electrical Engineering (EE) exam

Similar Electrical Engineering (EE) Doubts

Top Courses for Electrical Engineering (EE)

A 500 MW, 21 kV, 50 Hz, 3-phase, 2-pole synchronous generator having a rated pf = 0.9, has a moment of inertia of 27.5 x 103 kg-m2. The inertia constant (H, in sec) will be _____. (Answer up to two decimal places)Correct answer is '2.44'. Can you explain this answer?
Question Description
A 500 MW, 21 kV, 50 Hz, 3-phase, 2-pole synchronous generator having a rated pf = 0.9, has a moment of inertia of 27.5 x 103 kg-m2. The inertia constant (H, in sec) will be _____. (Answer up to two decimal places)Correct answer is '2.44'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A 500 MW, 21 kV, 50 Hz, 3-phase, 2-pole synchronous generator having a rated pf = 0.9, has a moment of inertia of 27.5 x 103 kg-m2. The inertia constant (H, in sec) will be _____. (Answer up to two decimal places)Correct answer is '2.44'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A 500 MW, 21 kV, 50 Hz, 3-phase, 2-pole synchronous generator having a rated pf = 0.9, has a moment of inertia of 27.5 x 103 kg-m2. The inertia constant (H, in sec) will be _____. (Answer up to two decimal places)Correct answer is '2.44'. Can you explain this answer?.
Solutions for A 500 MW, 21 kV, 50 Hz, 3-phase, 2-pole synchronous generator having a rated pf = 0.9, has a moment of inertia of 27.5 x 103 kg-m2. The inertia constant (H, in sec) will be _____. (Answer up to two decimal places)Correct answer is '2.44'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of A 500 MW, 21 kV, 50 Hz, 3-phase, 2-pole synchronous generator having a rated pf = 0.9, has a moment of inertia of 27.5 x 103 kg-m2. The inertia constant (H, in sec) will be _____. (Answer up to two decimal places)Correct answer is '2.44'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A 500 MW, 21 kV, 50 Hz, 3-phase, 2-pole synchronous generator having a rated pf = 0.9, has a moment of inertia of 27.5 x 103 kg-m2. The inertia constant (H, in sec) will be _____. (Answer up to two decimal places)Correct answer is '2.44'. Can you explain this answer?, a detailed solution for A 500 MW, 21 kV, 50 Hz, 3-phase, 2-pole synchronous generator having a rated pf = 0.9, has a moment of inertia of 27.5 x 103 kg-m2. The inertia constant (H, in sec) will be _____. (Answer up to two decimal places)Correct answer is '2.44'. Can you explain this answer? has been provided alongside types of A 500 MW, 21 kV, 50 Hz, 3-phase, 2-pole synchronous generator having a rated pf = 0.9, has a moment of inertia of 27.5 x 103 kg-m2. The inertia constant (H, in sec) will be _____. (Answer up to two decimal places)Correct answer is '2.44'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A 500 MW, 21 kV, 50 Hz, 3-phase, 2-pole synchronous generator having a rated pf = 0.9, has a moment of inertia of 27.5 x 103 kg-m2. The inertia constant (H, in sec) will be _____. (Answer up to two decimal places)Correct answer is '2.44'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev