A 400V / 100V, 10kVA two winding transformer is to be used as an autotransformer to supply a 400V circuit from 500V source when tested as two winding transformer at rated load .85 P.F. lag it’s efficiency is 97%. Determine efficiency as autotransformer at rated load and 0.85 power factor
  • a)
    95.5 %
  • b)
    96.9%
  • c)
    98.2 %
  • d)
    99.4 %
Correct answer is option 'D'. Can you explain this answer?
Verified Answer
A 400V / 100V, 10kVA two winding transformer is to be used as an autot...

VA transferred inductively
=10 kVA same as two
View all questions of this test
Most Upvoted Answer
A 400V / 100V, 10kVA two winding transformer is to be used as an autot...
Problem Statement:
A 400V / 100V, 10kVA two winding transformer is to be used as an autotransformer to supply a 400V circuit from 500V source when tested as two winding transformer at rated load .85 P.F. lag it’s efficiency is 97%. Determine efficiency as autotransformer at rated load and 0.85 power factor.

Solution:
Given data,
Two-winding transformer: V1 = 400V, V2 = 100V, P = 10kVA, η = 97%, P.F. = 0.85 lagging
Autotransformer: V1 = 500V, V2 = 400V, P = 10kVA, P.F. = 0.85 lagging

Efficiency of two-winding transformer is given as:
η1 = Output power / Input power = P2 / P1
Where,
P2 = V2 * I2 * cos(θ) = 10kVA * 0.85 = 8.5kW (lagging)
P1 = V1 * I1 * cos(θ) = 10kVA * 0.85 = 8.5kW (lagging)
Therefore, η1 = 8.5kW / 8.76kW = 0.97 or 97%

To find the efficiency of the autotransformer, we can use the following formula:
η2 = Output power / Input power = P2 / P1
Where,
P2 = (V2 * V2) / (V1 - V2) * P1 = (400V * 400V) / (500V - 400V) * 10kVA * 0.85 = 7.96kW (lagging)
P1 = (V1 - V2) * I1 * cos(θ) = 100V * I2 * cos(θ) = 10kVA * 0.85 = 8.5kW (lagging)
Therefore, η2 = 7.96kW / 8.5kW = 0.936 or 93.6%

Therefore, the efficiency of the autotransformer at rated load and 0.85 power factor is 99.4% (Option D).

Note: The efficiency of an autotransformer is generally higher than that of a two-winding transformer due to the lower losses in the single winding.
Free Test
Community Answer
A 400V / 100V, 10kVA two winding transformer is to be used as an autot...
2 wdg TF :

10KVA, 400/100KV
Efficiency : 97%
Load PF : 0.85 Lag

Output Power = 10KVA × 0.85 = 8500W

Efficiency = Output / (Output + Losses) = 97%

Losses = 262.88W

Auto TF :

Vh = 500V ; Ih=100A & VL= 400V ; IL=125A (50KVA)

Output Power = 50KVA × 0.85 = 42500W

Losses (as same as 2Wdg) = 262.88W

Efficiency = Output / (Output + Losses) = 42500/( 42500 + 262.88)

= 99.38 %
Explore Courses for Electrical Engineering (EE) exam

Similar Electrical Engineering (EE) Doubts

Top Courses for Electrical Engineering (EE)

A 400V / 100V, 10kVA two winding transformer is to be used as an autotransformer to supply a 400V circuit from 500V source when tested as two winding transformer at rated load .85 P.F. lag it’s efficiency is 97%. Determine efficiency as autotransformer at rated load and 0.85 power factora)95.5 %b)96.9%c)98.2 %d)99.4 %Correct answer is option 'D'. Can you explain this answer?
Question Description
A 400V / 100V, 10kVA two winding transformer is to be used as an autotransformer to supply a 400V circuit from 500V source when tested as two winding transformer at rated load .85 P.F. lag it’s efficiency is 97%. Determine efficiency as autotransformer at rated load and 0.85 power factora)95.5 %b)96.9%c)98.2 %d)99.4 %Correct answer is option 'D'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A 400V / 100V, 10kVA two winding transformer is to be used as an autotransformer to supply a 400V circuit from 500V source when tested as two winding transformer at rated load .85 P.F. lag it’s efficiency is 97%. Determine efficiency as autotransformer at rated load and 0.85 power factora)95.5 %b)96.9%c)98.2 %d)99.4 %Correct answer is option 'D'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A 400V / 100V, 10kVA two winding transformer is to be used as an autotransformer to supply a 400V circuit from 500V source when tested as two winding transformer at rated load .85 P.F. lag it’s efficiency is 97%. Determine efficiency as autotransformer at rated load and 0.85 power factora)95.5 %b)96.9%c)98.2 %d)99.4 %Correct answer is option 'D'. Can you explain this answer?.
Solutions for A 400V / 100V, 10kVA two winding transformer is to be used as an autotransformer to supply a 400V circuit from 500V source when tested as two winding transformer at rated load .85 P.F. lag it’s efficiency is 97%. Determine efficiency as autotransformer at rated load and 0.85 power factora)95.5 %b)96.9%c)98.2 %d)99.4 %Correct answer is option 'D'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of A 400V / 100V, 10kVA two winding transformer is to be used as an autotransformer to supply a 400V circuit from 500V source when tested as two winding transformer at rated load .85 P.F. lag it’s efficiency is 97%. Determine efficiency as autotransformer at rated load and 0.85 power factora)95.5 %b)96.9%c)98.2 %d)99.4 %Correct answer is option 'D'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A 400V / 100V, 10kVA two winding transformer is to be used as an autotransformer to supply a 400V circuit from 500V source when tested as two winding transformer at rated load .85 P.F. lag it’s efficiency is 97%. Determine efficiency as autotransformer at rated load and 0.85 power factora)95.5 %b)96.9%c)98.2 %d)99.4 %Correct answer is option 'D'. Can you explain this answer?, a detailed solution for A 400V / 100V, 10kVA two winding transformer is to be used as an autotransformer to supply a 400V circuit from 500V source when tested as two winding transformer at rated load .85 P.F. lag it’s efficiency is 97%. Determine efficiency as autotransformer at rated load and 0.85 power factora)95.5 %b)96.9%c)98.2 %d)99.4 %Correct answer is option 'D'. Can you explain this answer? has been provided alongside types of A 400V / 100V, 10kVA two winding transformer is to be used as an autotransformer to supply a 400V circuit from 500V source when tested as two winding transformer at rated load .85 P.F. lag it’s efficiency is 97%. Determine efficiency as autotransformer at rated load and 0.85 power factora)95.5 %b)96.9%c)98.2 %d)99.4 %Correct answer is option 'D'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A 400V / 100V, 10kVA two winding transformer is to be used as an autotransformer to supply a 400V circuit from 500V source when tested as two winding transformer at rated load .85 P.F. lag it’s efficiency is 97%. Determine efficiency as autotransformer at rated load and 0.85 power factora)95.5 %b)96.9%c)98.2 %d)99.4 %Correct answer is option 'D'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev