GATE Exam  >  GATE Questions  >  A two generator station supplies a feeder thr... Start Learning for Free
A two generator station supplies a feeder through a bus shown in figure. Additional power is fed to the bus through a transformer from a large system which may be regarded as infinite. A reactor X is included between the transformer and the bus to limit the SC rupturing capacity of the feeder circuit breaker B to 333 MVA (fault close to breaker). Find the inductive reactance of the reactor required.
System data are:
Generator G1: 25 MVA, 15% reactance
Generator G2: 50 MVA, 20% reactance
Transformer T1: 100 MVA, 8% reactance
Transformer T2: 40 MVA, 10% reactance
Assume that all reactance are given an appropriate voltage bases. Choose a base of 100 MVA.
  • a)
    2.39 pu
  • b)
    3.61 pu
  • c)
    1.45 pu
  • d)
    1.83 pu
Correct answer is option 'A'. Can you explain this answer?
Verified Answer
A two generator station supplies a feeder through a bus shown in figur...

All reactance are given an approximate voltage bases.
Perrault no load voltage = 1 pu
Base = 100 MVA
SC rupturing capacity of breaker 
Equivalent system reactance 
Equivalent system reactance at generator bus
= 0.3 - 0.08 = 0.22 pu
View all questions of this test
Explore Courses for GATE exam
A two generator station supplies a feeder through a bus shown in figure. Additional power is fed to the bus through a transformer from a large system which may be regarded as infinite. A reactor X is included between the transformer and the bus to limit the SC rupturing capacity of the feeder circuit breaker B to 333 MVA (fault close to breaker). Find the inductive reactance of the reactor required.System data are:Generator G1: 25 MVA, 15% reactanceGenerator G2: 50 MVA, 20% reactanceTransformer T1: 100 MVA, 8% reactanceTransformer T2: 40 MVA, 10% reactanceAssume that all reactance are given an appropriate voltage bases. Choose a base of 100 MVA.a)2.39 pub)3.61 puc)1.45 pud)1.83 puCorrect answer is option 'A'. Can you explain this answer?
Question Description
A two generator station supplies a feeder through a bus shown in figure. Additional power is fed to the bus through a transformer from a large system which may be regarded as infinite. A reactor X is included between the transformer and the bus to limit the SC rupturing capacity of the feeder circuit breaker B to 333 MVA (fault close to breaker). Find the inductive reactance of the reactor required.System data are:Generator G1: 25 MVA, 15% reactanceGenerator G2: 50 MVA, 20% reactanceTransformer T1: 100 MVA, 8% reactanceTransformer T2: 40 MVA, 10% reactanceAssume that all reactance are given an appropriate voltage bases. Choose a base of 100 MVA.a)2.39 pub)3.61 puc)1.45 pud)1.83 puCorrect answer is option 'A'. Can you explain this answer? for GATE 2024 is part of GATE preparation. The Question and answers have been prepared according to the GATE exam syllabus. Information about A two generator station supplies a feeder through a bus shown in figure. Additional power is fed to the bus through a transformer from a large system which may be regarded as infinite. A reactor X is included between the transformer and the bus to limit the SC rupturing capacity of the feeder circuit breaker B to 333 MVA (fault close to breaker). Find the inductive reactance of the reactor required.System data are:Generator G1: 25 MVA, 15% reactanceGenerator G2: 50 MVA, 20% reactanceTransformer T1: 100 MVA, 8% reactanceTransformer T2: 40 MVA, 10% reactanceAssume that all reactance are given an appropriate voltage bases. Choose a base of 100 MVA.a)2.39 pub)3.61 puc)1.45 pud)1.83 puCorrect answer is option 'A'. Can you explain this answer? covers all topics & solutions for GATE 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A two generator station supplies a feeder through a bus shown in figure. Additional power is fed to the bus through a transformer from a large system which may be regarded as infinite. A reactor X is included between the transformer and the bus to limit the SC rupturing capacity of the feeder circuit breaker B to 333 MVA (fault close to breaker). Find the inductive reactance of the reactor required.System data are:Generator G1: 25 MVA, 15% reactanceGenerator G2: 50 MVA, 20% reactanceTransformer T1: 100 MVA, 8% reactanceTransformer T2: 40 MVA, 10% reactanceAssume that all reactance are given an appropriate voltage bases. Choose a base of 100 MVA.a)2.39 pub)3.61 puc)1.45 pud)1.83 puCorrect answer is option 'A'. Can you explain this answer?.
Solutions for A two generator station supplies a feeder through a bus shown in figure. Additional power is fed to the bus through a transformer from a large system which may be regarded as infinite. A reactor X is included between the transformer and the bus to limit the SC rupturing capacity of the feeder circuit breaker B to 333 MVA (fault close to breaker). Find the inductive reactance of the reactor required.System data are:Generator G1: 25 MVA, 15% reactanceGenerator G2: 50 MVA, 20% reactanceTransformer T1: 100 MVA, 8% reactanceTransformer T2: 40 MVA, 10% reactanceAssume that all reactance are given an appropriate voltage bases. Choose a base of 100 MVA.a)2.39 pub)3.61 puc)1.45 pud)1.83 puCorrect answer is option 'A'. Can you explain this answer? in English & in Hindi are available as part of our courses for GATE. Download more important topics, notes, lectures and mock test series for GATE Exam by signing up for free.
Here you can find the meaning of A two generator station supplies a feeder through a bus shown in figure. Additional power is fed to the bus through a transformer from a large system which may be regarded as infinite. A reactor X is included between the transformer and the bus to limit the SC rupturing capacity of the feeder circuit breaker B to 333 MVA (fault close to breaker). Find the inductive reactance of the reactor required.System data are:Generator G1: 25 MVA, 15% reactanceGenerator G2: 50 MVA, 20% reactanceTransformer T1: 100 MVA, 8% reactanceTransformer T2: 40 MVA, 10% reactanceAssume that all reactance are given an appropriate voltage bases. Choose a base of 100 MVA.a)2.39 pub)3.61 puc)1.45 pud)1.83 puCorrect answer is option 'A'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A two generator station supplies a feeder through a bus shown in figure. Additional power is fed to the bus through a transformer from a large system which may be regarded as infinite. A reactor X is included between the transformer and the bus to limit the SC rupturing capacity of the feeder circuit breaker B to 333 MVA (fault close to breaker). Find the inductive reactance of the reactor required.System data are:Generator G1: 25 MVA, 15% reactanceGenerator G2: 50 MVA, 20% reactanceTransformer T1: 100 MVA, 8% reactanceTransformer T2: 40 MVA, 10% reactanceAssume that all reactance are given an appropriate voltage bases. Choose a base of 100 MVA.a)2.39 pub)3.61 puc)1.45 pud)1.83 puCorrect answer is option 'A'. Can you explain this answer?, a detailed solution for A two generator station supplies a feeder through a bus shown in figure. Additional power is fed to the bus through a transformer from a large system which may be regarded as infinite. A reactor X is included between the transformer and the bus to limit the SC rupturing capacity of the feeder circuit breaker B to 333 MVA (fault close to breaker). Find the inductive reactance of the reactor required.System data are:Generator G1: 25 MVA, 15% reactanceGenerator G2: 50 MVA, 20% reactanceTransformer T1: 100 MVA, 8% reactanceTransformer T2: 40 MVA, 10% reactanceAssume that all reactance are given an appropriate voltage bases. Choose a base of 100 MVA.a)2.39 pub)3.61 puc)1.45 pud)1.83 puCorrect answer is option 'A'. Can you explain this answer? has been provided alongside types of A two generator station supplies a feeder through a bus shown in figure. Additional power is fed to the bus through a transformer from a large system which may be regarded as infinite. A reactor X is included between the transformer and the bus to limit the SC rupturing capacity of the feeder circuit breaker B to 333 MVA (fault close to breaker). Find the inductive reactance of the reactor required.System data are:Generator G1: 25 MVA, 15% reactanceGenerator G2: 50 MVA, 20% reactanceTransformer T1: 100 MVA, 8% reactanceTransformer T2: 40 MVA, 10% reactanceAssume that all reactance are given an appropriate voltage bases. Choose a base of 100 MVA.a)2.39 pub)3.61 puc)1.45 pud)1.83 puCorrect answer is option 'A'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A two generator station supplies a feeder through a bus shown in figure. Additional power is fed to the bus through a transformer from a large system which may be regarded as infinite. A reactor X is included between the transformer and the bus to limit the SC rupturing capacity of the feeder circuit breaker B to 333 MVA (fault close to breaker). Find the inductive reactance of the reactor required.System data are:Generator G1: 25 MVA, 15% reactanceGenerator G2: 50 MVA, 20% reactanceTransformer T1: 100 MVA, 8% reactanceTransformer T2: 40 MVA, 10% reactanceAssume that all reactance are given an appropriate voltage bases. Choose a base of 100 MVA.a)2.39 pub)3.61 puc)1.45 pud)1.83 puCorrect answer is option 'A'. Can you explain this answer? tests, examples and also practice GATE tests.