GATE Exam  >  GATE Questions  >  An alternator rated at 6.6 kV protected by ba... Start Learning for Free
An alternator rated at 6.6 kV protected by balanced circulating current system has its neutral grounded through current system has its neutral grounded through a resistance of 10 Ω. The protective relay is set to operate when there is out of balance current of 1 A in pilot wires which are connected to secondary winding of 800/5 ratio current transformer. The percentage of winding which remains unprotected is______
      Correct answer is between '41,43'. Can you explain this answer?
      Verified Answer
      An alternator rated at 6.6 kV protected by balanced circulating curren...
      Let x% be the percentage of winding which remains unprotected
      The voltage of unprotected winding 

      View all questions of this test
      Most Upvoted Answer
      An alternator rated at 6.6 kV protected by balanced circulating curren...
      Ohms. The rated current of the alternator is 500 A.
      Explore Courses for GATE exam

      Similar GATE Doubts

      An alternator rated at 6.6 kV protected by balanced circulating current system has its neutral grounded through current system has its neutral grounded through a resistance of 10 Ω. The protective relay is set to operate when there is out of balance current of 1 A in pilot wires which are connected to secondary winding of 800/5 ratio current transformer. The percentage of winding which remains unprotected is______Correct answer is between '41,43'. Can you explain this answer?
      Question Description
      An alternator rated at 6.6 kV protected by balanced circulating current system has its neutral grounded through current system has its neutral grounded through a resistance of 10 Ω. The protective relay is set to operate when there is out of balance current of 1 A in pilot wires which are connected to secondary winding of 800/5 ratio current transformer. The percentage of winding which remains unprotected is______Correct answer is between '41,43'. Can you explain this answer? for GATE 2024 is part of GATE preparation. The Question and answers have been prepared according to the GATE exam syllabus. Information about An alternator rated at 6.6 kV protected by balanced circulating current system has its neutral grounded through current system has its neutral grounded through a resistance of 10 Ω. The protective relay is set to operate when there is out of balance current of 1 A in pilot wires which are connected to secondary winding of 800/5 ratio current transformer. The percentage of winding which remains unprotected is______Correct answer is between '41,43'. Can you explain this answer? covers all topics & solutions for GATE 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for An alternator rated at 6.6 kV protected by balanced circulating current system has its neutral grounded through current system has its neutral grounded through a resistance of 10 Ω. The protective relay is set to operate when there is out of balance current of 1 A in pilot wires which are connected to secondary winding of 800/5 ratio current transformer. The percentage of winding which remains unprotected is______Correct answer is between '41,43'. Can you explain this answer?.
      Solutions for An alternator rated at 6.6 kV protected by balanced circulating current system has its neutral grounded through current system has its neutral grounded through a resistance of 10 Ω. The protective relay is set to operate when there is out of balance current of 1 A in pilot wires which are connected to secondary winding of 800/5 ratio current transformer. The percentage of winding which remains unprotected is______Correct answer is between '41,43'. Can you explain this answer? in English & in Hindi are available as part of our courses for GATE. Download more important topics, notes, lectures and mock test series for GATE Exam by signing up for free.
      Here you can find the meaning of An alternator rated at 6.6 kV protected by balanced circulating current system has its neutral grounded through current system has its neutral grounded through a resistance of 10 Ω. The protective relay is set to operate when there is out of balance current of 1 A in pilot wires which are connected to secondary winding of 800/5 ratio current transformer. The percentage of winding which remains unprotected is______Correct answer is between '41,43'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of An alternator rated at 6.6 kV protected by balanced circulating current system has its neutral grounded through current system has its neutral grounded through a resistance of 10 Ω. The protective relay is set to operate when there is out of balance current of 1 A in pilot wires which are connected to secondary winding of 800/5 ratio current transformer. The percentage of winding which remains unprotected is______Correct answer is between '41,43'. Can you explain this answer?, a detailed solution for An alternator rated at 6.6 kV protected by balanced circulating current system has its neutral grounded through current system has its neutral grounded through a resistance of 10 Ω. The protective relay is set to operate when there is out of balance current of 1 A in pilot wires which are connected to secondary winding of 800/5 ratio current transformer. The percentage of winding which remains unprotected is______Correct answer is between '41,43'. Can you explain this answer? has been provided alongside types of An alternator rated at 6.6 kV protected by balanced circulating current system has its neutral grounded through current system has its neutral grounded through a resistance of 10 Ω. The protective relay is set to operate when there is out of balance current of 1 A in pilot wires which are connected to secondary winding of 800/5 ratio current transformer. The percentage of winding which remains unprotected is______Correct answer is between '41,43'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice An alternator rated at 6.6 kV protected by balanced circulating current system has its neutral grounded through current system has its neutral grounded through a resistance of 10 Ω. The protective relay is set to operate when there is out of balance current of 1 A in pilot wires which are connected to secondary winding of 800/5 ratio current transformer. The percentage of winding which remains unprotected is______Correct answer is between '41,43'. Can you explain this answer? tests, examples and also practice GATE tests.
      Explore Courses for GATE exam
      Signup for Free!
      Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
      10M+ students study on EduRev