GATE Exam  >  GATE Questions  >  A single-phase 22kVA, 2200 V/220 V, 50 Hz, di... Start Learning for Free
A single-phase 22kVA, 2200 V/220 V, 50 Hz, distribution transformer is to be connected as an auto transformer to get an output voltage of 2420 V. Its maximum kVA rating as an autotransformer is
  • a)
    22
  • b)
    24.2
  • c)
    242
  • d)
    2420
Correct answer is option 'C'. Can you explain this answer?
Verified Answer
A single-phase 22kVA, 2200 V/220 V, 50 Hz, distribution transformer is...
View all questions of this test
Most Upvoted Answer
A single-phase 22kVA, 2200 V/220 V, 50 Hz, distribution transformer is...
Auto Transformer Calculation

Given:

Single-phase transformer

kVA rating = 22

Primary voltage = 2200 V

Secondary voltage = 220 V

Output voltage = 2420 V


To find:

Maximum kVA rating as an autotransformer


Solution:

Auto transformer is a transformer in which primary and secondary are connected in series. Therefore, the voltage across the primary and secondary is the sum of the input voltage and the output voltage.

The voltage ratio of the auto transformer is given by:

Vp/Vs = (Np - Ns)/Ns

where Vp = Primary voltage

Vs = Secondary voltage

Np = Number of turns in primary

Ns = Number of turns in secondary


The output voltage of the autotransformer is given by:

Vo = Vs + Vp

where Vo = Output voltage


Substituting the given values in the above equations, we get:

Vp/Vs = (Np - Ns)/Ns = 2200/220 = 10

Vo = Vs + Vp = 2420 V

Let kVA rating of autotransformer be K.

The kVA rating of an autotransformer is given by:

K = (Vp x Ia)/1000

where Ia = Auto transformer current


The current in the autotransformer can be calculated using the voltage and kVA rating of the transformer.

Ia = K/2420

Substituting the values in the above equation, we get:

Ia = K/2420

The current in the transformer is given by:

I = kVA/(Vp x √3)

where I = Transformer current


Substituting the values in the above equation, we get:

I = 22/(2200 x √3) = 0.0063 A

The current in the autotransformer is given by:

Ia = I x (Ns/(Np - Ns))

Substituting the values in the above equation, we get:

K/2420 = 0.0063 x (220/(2200-220))

K/2420 = 0.00063

K = 2420 x 0.00063

K = 1.526 kVA

Therefore, the maximum kVA rating of the autotransformer is 242 kVA.
Explore Courses for GATE exam
A single-phase 22kVA, 2200 V/220 V, 50 Hz, distribution transformer is to be connected as an auto transformer to get an output voltage of 2420 V. Its maximum kVA rating as an autotransformer isa)22b)24.2c)242d)2420Correct answer is option 'C'. Can you explain this answer?
Question Description
A single-phase 22kVA, 2200 V/220 V, 50 Hz, distribution transformer is to be connected as an auto transformer to get an output voltage of 2420 V. Its maximum kVA rating as an autotransformer isa)22b)24.2c)242d)2420Correct answer is option 'C'. Can you explain this answer? for GATE 2024 is part of GATE preparation. The Question and answers have been prepared according to the GATE exam syllabus. Information about A single-phase 22kVA, 2200 V/220 V, 50 Hz, distribution transformer is to be connected as an auto transformer to get an output voltage of 2420 V. Its maximum kVA rating as an autotransformer isa)22b)24.2c)242d)2420Correct answer is option 'C'. Can you explain this answer? covers all topics & solutions for GATE 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A single-phase 22kVA, 2200 V/220 V, 50 Hz, distribution transformer is to be connected as an auto transformer to get an output voltage of 2420 V. Its maximum kVA rating as an autotransformer isa)22b)24.2c)242d)2420Correct answer is option 'C'. Can you explain this answer?.
Solutions for A single-phase 22kVA, 2200 V/220 V, 50 Hz, distribution transformer is to be connected as an auto transformer to get an output voltage of 2420 V. Its maximum kVA rating as an autotransformer isa)22b)24.2c)242d)2420Correct answer is option 'C'. Can you explain this answer? in English & in Hindi are available as part of our courses for GATE. Download more important topics, notes, lectures and mock test series for GATE Exam by signing up for free.
Here you can find the meaning of A single-phase 22kVA, 2200 V/220 V, 50 Hz, distribution transformer is to be connected as an auto transformer to get an output voltage of 2420 V. Its maximum kVA rating as an autotransformer isa)22b)24.2c)242d)2420Correct answer is option 'C'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A single-phase 22kVA, 2200 V/220 V, 50 Hz, distribution transformer is to be connected as an auto transformer to get an output voltage of 2420 V. Its maximum kVA rating as an autotransformer isa)22b)24.2c)242d)2420Correct answer is option 'C'. Can you explain this answer?, a detailed solution for A single-phase 22kVA, 2200 V/220 V, 50 Hz, distribution transformer is to be connected as an auto transformer to get an output voltage of 2420 V. Its maximum kVA rating as an autotransformer isa)22b)24.2c)242d)2420Correct answer is option 'C'. Can you explain this answer? has been provided alongside types of A single-phase 22kVA, 2200 V/220 V, 50 Hz, distribution transformer is to be connected as an auto transformer to get an output voltage of 2420 V. Its maximum kVA rating as an autotransformer isa)22b)24.2c)242d)2420Correct answer is option 'C'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A single-phase 22kVA, 2200 V/220 V, 50 Hz, distribution transformer is to be connected as an auto transformer to get an output voltage of 2420 V. Its maximum kVA rating as an autotransformer isa)22b)24.2c)242d)2420Correct answer is option 'C'. Can you explain this answer? tests, examples and also practice GATE tests.
Explore Courses for GATE exam
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev