A cylindrical rotor synchronous generator has steady state synchronous reactance of 0.7 pu and subtransient reactance of 0.2 pu. It is operating at (1+ j0) pu terminal voltage with an internal emf of (1 + j0.7) pu. Following a three-phase solid short circuit fault at the terminal of the generator, the magnitude of the subtransient internal emf (rounded off to 2 decimal places) is ________ pu.
    Correct answer is '1.02'. Can you explain this answer?
    Verified Answer
    A cylindrical rotor synchronous generator has steady state synchronous...
    Prefault current, 
    Subtransient induced emf,
    View all questions of this test
    Most Upvoted Answer
    A cylindrical rotor synchronous generator has steady state synchronous...
    Given:

    • Steady state synchronous reactance (Xs) = 0.7 pu

    • Subtransient reactance (X"d) = 0.2 pu

    • Terminal voltage = 1 + j0 pu

    • Internal emf = 1 + j0.7 pu



    Calculation:

    • During the fault, the fault current causes a sudden drop in the terminal voltage of the generator, leading to a sudden change in the internal emf.

    • The subtransient internal emf is given by E" = E - jX"dI, where E is the internal emf before the fault and I is the fault current.

    • The fault current can be calculated using the Thevenin equivalent of the generator. The Thevenin voltage is equal to the terminal voltage, and the Thevenin impedance is equal to the synchronous reactance Xs.

    • The fault current is given by I = E_th/Xs, where E_th is the Thevenin voltage.

    • Substituting the given values, we get I = (1 + j0)/(0.7) = 1.429 - j0.714 pu.

    • Substituting the values of E, X"d, and I, we get E" = (1 + j0.7) - j(0.2)(1.429 - j0.714) = 1.02 + j0.226 pu.

    • Rounding off to two decimal places, we get E" = 1.02 pu.



    Therefore, the magnitude of the subtransient internal emf is 1.02 pu.
    Explore Courses for GATE exam

    Similar GATE Doubts

    A cylindrical rotor synchronous generator has steady state synchronous reactance of 0.7 pu and subtransient reactance of 0.2 pu. It is operating at (1+ j0) pu terminal voltage with an internal emf of (1 + j0.7) pu. Following a three-phase solid short circuit fault at the terminal of the generator, the magnitude of the subtransient internal emf (rounded off to 2 decimal places) is ________ pu.Correct answer is '1.02'. Can you explain this answer?
    Question Description
    A cylindrical rotor synchronous generator has steady state synchronous reactance of 0.7 pu and subtransient reactance of 0.2 pu. It is operating at (1+ j0) pu terminal voltage with an internal emf of (1 + j0.7) pu. Following a three-phase solid short circuit fault at the terminal of the generator, the magnitude of the subtransient internal emf (rounded off to 2 decimal places) is ________ pu.Correct answer is '1.02'. Can you explain this answer? for GATE 2024 is part of GATE preparation. The Question and answers have been prepared according to the GATE exam syllabus. Information about A cylindrical rotor synchronous generator has steady state synchronous reactance of 0.7 pu and subtransient reactance of 0.2 pu. It is operating at (1+ j0) pu terminal voltage with an internal emf of (1 + j0.7) pu. Following a three-phase solid short circuit fault at the terminal of the generator, the magnitude of the subtransient internal emf (rounded off to 2 decimal places) is ________ pu.Correct answer is '1.02'. Can you explain this answer? covers all topics & solutions for GATE 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A cylindrical rotor synchronous generator has steady state synchronous reactance of 0.7 pu and subtransient reactance of 0.2 pu. It is operating at (1+ j0) pu terminal voltage with an internal emf of (1 + j0.7) pu. Following a three-phase solid short circuit fault at the terminal of the generator, the magnitude of the subtransient internal emf (rounded off to 2 decimal places) is ________ pu.Correct answer is '1.02'. Can you explain this answer?.
    Solutions for A cylindrical rotor synchronous generator has steady state synchronous reactance of 0.7 pu and subtransient reactance of 0.2 pu. It is operating at (1+ j0) pu terminal voltage with an internal emf of (1 + j0.7) pu. Following a three-phase solid short circuit fault at the terminal of the generator, the magnitude of the subtransient internal emf (rounded off to 2 decimal places) is ________ pu.Correct answer is '1.02'. Can you explain this answer? in English & in Hindi are available as part of our courses for GATE. Download more important topics, notes, lectures and mock test series for GATE Exam by signing up for free.
    Here you can find the meaning of A cylindrical rotor synchronous generator has steady state synchronous reactance of 0.7 pu and subtransient reactance of 0.2 pu. It is operating at (1+ j0) pu terminal voltage with an internal emf of (1 + j0.7) pu. Following a three-phase solid short circuit fault at the terminal of the generator, the magnitude of the subtransient internal emf (rounded off to 2 decimal places) is ________ pu.Correct answer is '1.02'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A cylindrical rotor synchronous generator has steady state synchronous reactance of 0.7 pu and subtransient reactance of 0.2 pu. It is operating at (1+ j0) pu terminal voltage with an internal emf of (1 + j0.7) pu. Following a three-phase solid short circuit fault at the terminal of the generator, the magnitude of the subtransient internal emf (rounded off to 2 decimal places) is ________ pu.Correct answer is '1.02'. Can you explain this answer?, a detailed solution for A cylindrical rotor synchronous generator has steady state synchronous reactance of 0.7 pu and subtransient reactance of 0.2 pu. It is operating at (1+ j0) pu terminal voltage with an internal emf of (1 + j0.7) pu. Following a three-phase solid short circuit fault at the terminal of the generator, the magnitude of the subtransient internal emf (rounded off to 2 decimal places) is ________ pu.Correct answer is '1.02'. Can you explain this answer? has been provided alongside types of A cylindrical rotor synchronous generator has steady state synchronous reactance of 0.7 pu and subtransient reactance of 0.2 pu. It is operating at (1+ j0) pu terminal voltage with an internal emf of (1 + j0.7) pu. Following a three-phase solid short circuit fault at the terminal of the generator, the magnitude of the subtransient internal emf (rounded off to 2 decimal places) is ________ pu.Correct answer is '1.02'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A cylindrical rotor synchronous generator has steady state synchronous reactance of 0.7 pu and subtransient reactance of 0.2 pu. It is operating at (1+ j0) pu terminal voltage with an internal emf of (1 + j0.7) pu. Following a three-phase solid short circuit fault at the terminal of the generator, the magnitude of the subtransient internal emf (rounded off to 2 decimal places) is ________ pu.Correct answer is '1.02'. Can you explain this answer? tests, examples and also practice GATE tests.
    Explore Courses for GATE exam
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev