Full load efficiency of a 100 kVA transformer is 98%. Maximum efficiency occurs at (3/4)×full load. The power factor is 0.8 lagging at all loads. ?)
1.Estimate the copper loss (in W) at full load.
2.Estimate the iron loss (in W).
3.Estimate the percentage efficiency in half load.?
Most Upvoted Answer
Full load efficiency of a 100 kVA transformer is 98%. Maximum efficien...
Estimating Losses and Efficiency of a Transformer

Given:
- Transformer rating: 100 kVA
- Full load efficiency: 98%
- Maximum efficiency occurs at (3/4) x full load
- Power factor: 0.8 lagging at all loads

1. Estimating Copper Loss at Full Load
- Copper loss is the power loss due to the resistance of the transformer windings.
- Copper loss can be calculated using the formula: I^2R, where I is the current and R is the resistance.
- At full load, the transformer output power is 100 kVA, and the efficiency is 98%, so the input power is:
Input power = Output power / Efficiency
= 100 kVA / 0.98
= 102.04 kVA
- The input current can be calculated using the formula: Input power / (sqrt(3) x Input voltage x Power factor)
- At full load, the input voltage is assumed to be equal to the rated voltage of the transformer, which is 100 kV / sqrt(3) = 57.74 kV.
- Therefore, the input current at full load is:
Input current = 102.04 kVA / (sqrt(3) x 57.74 kV x 0.8)
= 1,293.9 A
- Let's assume that the resistance of the transformer windings is 0.1 ohm.
- Therefore, the copper loss at full load is:
Copper loss = I^2R
= (1,293.9 A)^2 x 0.1 ohm
= 167,351.3 W or 167.4 kW

2. Estimating Iron Loss
- Iron loss is the power loss due to the hysteresis and eddy currents in the transformer core.
- Iron loss is usually expressed as a percentage of the transformer rating.
- Let's assume that the iron loss is 2% of the transformer rating.
- Therefore, the iron loss is:
Iron loss = 2% x 100 kVA
= 2,000 W or 2 kW

3. Estimating Percentage Efficiency at Half Load
- At (3/4) x full load, the efficiency of the transformer is maximum.
- Therefore, the efficiency at (3/4) x full load is:
Efficiency at (3/4) x full load = 98%
- Let's assume that the load on the transformer is halved, i.e., 50 kVA.
- The input current at half load can be calculated using the same formula as before:
Input current at half load = 50 kVA / (sqrt(3) x 57.74 kV x 0.8)
= 647.0 A
- The copper loss at half load can be calculated using the formula: I^2R
Copper loss at half load = (647.0 A)^2 x 0.1 ohm
= 42,024.9 W or 42.0 kW
- The total losses at half load are:
Total losses at half load = Copper loss + Iron loss
= 42,024.9 W +
Community Answer
Full load efficiency of a 100 kVA transformer is 98%. Maximum efficien...
A
Explore Courses for GATE exam
Full load efficiency of a 100 kVA transformer is 98%. Maximum efficiency occurs at (3/4)×full load. The power factor is 0.8 lagging at all loads. ?) 1.Estimate the copper loss (in W) at full load. 2.Estimate the iron loss (in W). 3.Estimate the percentage efficiency in half load.?
Question Description
Full load efficiency of a 100 kVA transformer is 98%. Maximum efficiency occurs at (3/4)×full load. The power factor is 0.8 lagging at all loads. ?) 1.Estimate the copper loss (in W) at full load. 2.Estimate the iron loss (in W). 3.Estimate the percentage efficiency in half load.? for GATE 2024 is part of GATE preparation. The Question and answers have been prepared according to the GATE exam syllabus. Information about Full load efficiency of a 100 kVA transformer is 98%. Maximum efficiency occurs at (3/4)×full load. The power factor is 0.8 lagging at all loads. ?) 1.Estimate the copper loss (in W) at full load. 2.Estimate the iron loss (in W). 3.Estimate the percentage efficiency in half load.? covers all topics & solutions for GATE 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for Full load efficiency of a 100 kVA transformer is 98%. Maximum efficiency occurs at (3/4)×full load. The power factor is 0.8 lagging at all loads. ?) 1.Estimate the copper loss (in W) at full load. 2.Estimate the iron loss (in W). 3.Estimate the percentage efficiency in half load.?.
Solutions for Full load efficiency of a 100 kVA transformer is 98%. Maximum efficiency occurs at (3/4)×full load. The power factor is 0.8 lagging at all loads. ?) 1.Estimate the copper loss (in W) at full load. 2.Estimate the iron loss (in W). 3.Estimate the percentage efficiency in half load.? in English & in Hindi are available as part of our courses for GATE. Download more important topics, notes, lectures and mock test series for GATE Exam by signing up for free.
Here you can find the meaning of Full load efficiency of a 100 kVA transformer is 98%. Maximum efficiency occurs at (3/4)×full load. The power factor is 0.8 lagging at all loads. ?) 1.Estimate the copper loss (in W) at full load. 2.Estimate the iron loss (in W). 3.Estimate the percentage efficiency in half load.? defined & explained in the simplest way possible. Besides giving the explanation of Full load efficiency of a 100 kVA transformer is 98%. Maximum efficiency occurs at (3/4)×full load. The power factor is 0.8 lagging at all loads. ?) 1.Estimate the copper loss (in W) at full load. 2.Estimate the iron loss (in W). 3.Estimate the percentage efficiency in half load.?, a detailed solution for Full load efficiency of a 100 kVA transformer is 98%. Maximum efficiency occurs at (3/4)×full load. The power factor is 0.8 lagging at all loads. ?) 1.Estimate the copper loss (in W) at full load. 2.Estimate the iron loss (in W). 3.Estimate the percentage efficiency in half load.? has been provided alongside types of Full load efficiency of a 100 kVA transformer is 98%. Maximum efficiency occurs at (3/4)×full load. The power factor is 0.8 lagging at all loads. ?) 1.Estimate the copper loss (in W) at full load. 2.Estimate the iron loss (in W). 3.Estimate the percentage efficiency in half load.? theory, EduRev gives you an ample number of questions to practice Full load efficiency of a 100 kVA transformer is 98%. Maximum efficiency occurs at (3/4)×full load. The power factor is 0.8 lagging at all loads. ?) 1.Estimate the copper loss (in W) at full load. 2.Estimate the iron loss (in W). 3.Estimate the percentage efficiency in half load.? tests, examples and also practice GATE tests.
Explore Courses for GATE exam
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev