In a three phase system power measured by using two wattmeter method and total power measured by both wattmeter is 50kW and power factor is 0.5 lagging. Reading of second wattmeter is –
  • a)
    25 kW
  • b)
    0 kW
  • c)
    16.67 kW
  • d)
    33.33 kW
Correct answer is option 'B'. Can you explain this answer?
Verified Answer
In a three phase system power measured by using two wattmeter method a...
Total power,
P = 50kW
ϕ = 60 °
since at  ϕ = 60 ° one watt meter reads 0 watts  and entire power is reading by another watt meter 
so at this condition the reading of another watt meter is zero.
View all questions of this test
Most Upvoted Answer
In a three phase system power measured by using two wattmeter method a...
To find the reading of the second wattmeter, we can use the formula:

Total power = √3 * V * I * power factor

Given that the total power is 50 kW and the power factor is 0.5 lagging, we can rearrange the formula to solve for the product of V * I:

V * I = Total power / (√3 * power factor)

V * I = 50 kW / (√3 * 0.5)

V * I = 50 kW / (1.732 * 0.5)

V * I = 50 kW / 0.866

V * I ≈ 57.74 kVA

Since the power factor is lagging, the power triangle will look like this:

|\
| \
Reactive Power | \ Apparent Power
| \
|____\

The true power (or real power) is the horizontal component of the power triangle, which is the power measured by the two wattmeters.

Given that the power factor is lagging (0.5 lagging), the angle between the apparent power and the true power is 60 degrees.

Therefore, the reading of the second wattmeter can be found by multiplying the apparent power (V * I) by the sine of the angle between the true power and the apparent power:

Reading of second wattmeter = (V * I) * sin(60 degrees)

Reading of second wattmeter = (57.74 kVA) * sin(60 degrees)

Reading of second wattmeter ≈ 49.99 kVA

Therefore, the reading of the second wattmeter is approximately 49.99 kVA.
Explore Courses for SSC exam
In a three phase system power measured by using two wattmeter method and total power measured by both wattmeter is 50kW and power factor is 0.5 lagging. Reading of second wattmeter is –a)25 kWb)0 kWc)16.67 kWd)33.33 kWCorrect answer is option 'B'. Can you explain this answer?
Question Description
In a three phase system power measured by using two wattmeter method and total power measured by both wattmeter is 50kW and power factor is 0.5 lagging. Reading of second wattmeter is –a)25 kWb)0 kWc)16.67 kWd)33.33 kWCorrect answer is option 'B'. Can you explain this answer? for SSC 2024 is part of SSC preparation. The Question and answers have been prepared according to the SSC exam syllabus. Information about In a three phase system power measured by using two wattmeter method and total power measured by both wattmeter is 50kW and power factor is 0.5 lagging. Reading of second wattmeter is –a)25 kWb)0 kWc)16.67 kWd)33.33 kWCorrect answer is option 'B'. Can you explain this answer? covers all topics & solutions for SSC 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for In a three phase system power measured by using two wattmeter method and total power measured by both wattmeter is 50kW and power factor is 0.5 lagging. Reading of second wattmeter is –a)25 kWb)0 kWc)16.67 kWd)33.33 kWCorrect answer is option 'B'. Can you explain this answer?.
Solutions for In a three phase system power measured by using two wattmeter method and total power measured by both wattmeter is 50kW and power factor is 0.5 lagging. Reading of second wattmeter is –a)25 kWb)0 kWc)16.67 kWd)33.33 kWCorrect answer is option 'B'. Can you explain this answer? in English & in Hindi are available as part of our courses for SSC. Download more important topics, notes, lectures and mock test series for SSC Exam by signing up for free.
Here you can find the meaning of In a three phase system power measured by using two wattmeter method and total power measured by both wattmeter is 50kW and power factor is 0.5 lagging. Reading of second wattmeter is –a)25 kWb)0 kWc)16.67 kWd)33.33 kWCorrect answer is option 'B'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of In a three phase system power measured by using two wattmeter method and total power measured by both wattmeter is 50kW and power factor is 0.5 lagging. Reading of second wattmeter is –a)25 kWb)0 kWc)16.67 kWd)33.33 kWCorrect answer is option 'B'. Can you explain this answer?, a detailed solution for In a three phase system power measured by using two wattmeter method and total power measured by both wattmeter is 50kW and power factor is 0.5 lagging. Reading of second wattmeter is –a)25 kWb)0 kWc)16.67 kWd)33.33 kWCorrect answer is option 'B'. Can you explain this answer? has been provided alongside types of In a three phase system power measured by using two wattmeter method and total power measured by both wattmeter is 50kW and power factor is 0.5 lagging. Reading of second wattmeter is –a)25 kWb)0 kWc)16.67 kWd)33.33 kWCorrect answer is option 'B'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice In a three phase system power measured by using two wattmeter method and total power measured by both wattmeter is 50kW and power factor is 0.5 lagging. Reading of second wattmeter is –a)25 kWb)0 kWc)16.67 kWd)33.33 kWCorrect answer is option 'B'. Can you explain this answer? tests, examples and also practice SSC tests.
Explore Courses for SSC exam
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev