GATE Exam  >  GATE Questions  >   A 15 MVA, 11 kV, alternator has positive, ne... Start Learning for Free
A 15 MVA, 11 kV, alternator has positive, negative and zero sequence reactance are 0.3 p.u., 0.2 p.u. and 0.05 p.u. respectively. Find the value of resistance to be added in the generator neutral so that the fault current of LG fault does not exceed 1.5 times of rated line current.
  • a)
    2.3 Ω
  • b)
    0.641 Ω
  • c)
    5.17 Ω
  • d)
    8.34 Ω
Correct answer is option 'C'. Can you explain this answer?
Verified Answer
A 15 MVA, 11 kV, alternator has positive, negative and zero sequence ...
For L-G fault Current
Rn= 0.641 p.u.
R = 5.17 Ω
View all questions of this test
Most Upvoted Answer
A 15 MVA, 11 kV, alternator has positive, negative and zero sequence ...
Given data:
- MVA rating of alternator (S) = 15 MVA
- Voltage rating of alternator (V) = 11 kV
- Positive sequence reactance (X1) = 0.3 p.u.
- Negative sequence reactance (X2) = 0.2 p.u.
- Zero sequence reactance (X0) = 0.05 p.u.
- Fault current limit (If) = 1.5 times rated line current

To find:
- Resistance to be added in the generator neutral (Rn)

Solution:
1. Calculation of rated line current:
- Rated line current (I) = S / (sqrt(3) x V) = 15 x 10^6 / (sqrt(3) x 11 x 10^3) = 798.5 A

2. Calculation of fault current for LG fault:
- LG fault means a fault between one phase and ground (L-G)
- For LG fault, the fault current can be calculated using the following formula:
Ifault = (V / (sqrt(3) x Zf)) x (1 / (1 + Zn / Zf))
where,
Zf = Fault impedance = (X1 + X2 + X0)/3 = (0.3 + 0.2 + 0.05)/3 = 0.1833 p.u. (approx)
Zn = Neutral impedance = Rn + jX0
Ifault should not exceed 1.5 times rated line current

- Let's assume a value of Rn and calculate Ifault:
- Let Rn = 1 Ω
- Zn = Rn + jX0 = 1 + j0.05
- Ifault = (11 x 10^3 / (sqrt(3) x 0.1833)) x (1 / (1 + (1+j0.05) / 0.1833)) = 1565.6 A (approx)
- Since Ifault > 1.5 x I, this value of Rn is not acceptable

- We can solve this equation using an iterative method to find the value of Rn that satisfies the fault current limit. However, we can also use a simplified formula for approximate calculation:
Rn = (1 / (2 x pi x f x X0)) x (1 - sqrt(1 - (3 x Zf / Z1)^2))
where,
f = frequency = 50 Hz
Z1 = Positive sequence impedance = (X1 + R) = 0.3 + R (assuming negligible resistance in the generator)

- Substituting the given values and solving:
Rn = (1 / (2 x pi x 50 x 0.05)) x (1 - sqrt(1 - (3 x 0.1833 / (0.3 + R))^2))
Rn = 5.17 Ω (approx)

Answer:
The value of resistance to be added in the generator neutral so that the fault current of LG fault does not exceed 1.5 times of rated line current is 5.17 Ω (option c).
Explore Courses for GATE exam
A 15 MVA, 11 kV, alternator has positive, negative and zero sequence reactance are 0.3 p.u., 0.2 p.u. and 0.05 p.u. respectively. Find the value of resistance to be added in the generator neutral so that the fault current of LG fault does not exceed 1.5 times of rated line current.a)2.3 Ωb)0.641 Ωc)5.17 Ωd)8.34 ΩCorrect answer is option 'C'. Can you explain this answer?
Question Description
A 15 MVA, 11 kV, alternator has positive, negative and zero sequence reactance are 0.3 p.u., 0.2 p.u. and 0.05 p.u. respectively. Find the value of resistance to be added in the generator neutral so that the fault current of LG fault does not exceed 1.5 times of rated line current.a)2.3 Ωb)0.641 Ωc)5.17 Ωd)8.34 ΩCorrect answer is option 'C'. Can you explain this answer? for GATE 2024 is part of GATE preparation. The Question and answers have been prepared according to the GATE exam syllabus. Information about A 15 MVA, 11 kV, alternator has positive, negative and zero sequence reactance are 0.3 p.u., 0.2 p.u. and 0.05 p.u. respectively. Find the value of resistance to be added in the generator neutral so that the fault current of LG fault does not exceed 1.5 times of rated line current.a)2.3 Ωb)0.641 Ωc)5.17 Ωd)8.34 ΩCorrect answer is option 'C'. Can you explain this answer? covers all topics & solutions for GATE 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A 15 MVA, 11 kV, alternator has positive, negative and zero sequence reactance are 0.3 p.u., 0.2 p.u. and 0.05 p.u. respectively. Find the value of resistance to be added in the generator neutral so that the fault current of LG fault does not exceed 1.5 times of rated line current.a)2.3 Ωb)0.641 Ωc)5.17 Ωd)8.34 ΩCorrect answer is option 'C'. Can you explain this answer?.
Solutions for A 15 MVA, 11 kV, alternator has positive, negative and zero sequence reactance are 0.3 p.u., 0.2 p.u. and 0.05 p.u. respectively. Find the value of resistance to be added in the generator neutral so that the fault current of LG fault does not exceed 1.5 times of rated line current.a)2.3 Ωb)0.641 Ωc)5.17 Ωd)8.34 ΩCorrect answer is option 'C'. Can you explain this answer? in English & in Hindi are available as part of our courses for GATE. Download more important topics, notes, lectures and mock test series for GATE Exam by signing up for free.
Here you can find the meaning of A 15 MVA, 11 kV, alternator has positive, negative and zero sequence reactance are 0.3 p.u., 0.2 p.u. and 0.05 p.u. respectively. Find the value of resistance to be added in the generator neutral so that the fault current of LG fault does not exceed 1.5 times of rated line current.a)2.3 Ωb)0.641 Ωc)5.17 Ωd)8.34 ΩCorrect answer is option 'C'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A 15 MVA, 11 kV, alternator has positive, negative and zero sequence reactance are 0.3 p.u., 0.2 p.u. and 0.05 p.u. respectively. Find the value of resistance to be added in the generator neutral so that the fault current of LG fault does not exceed 1.5 times of rated line current.a)2.3 Ωb)0.641 Ωc)5.17 Ωd)8.34 ΩCorrect answer is option 'C'. Can you explain this answer?, a detailed solution for A 15 MVA, 11 kV, alternator has positive, negative and zero sequence reactance are 0.3 p.u., 0.2 p.u. and 0.05 p.u. respectively. Find the value of resistance to be added in the generator neutral so that the fault current of LG fault does not exceed 1.5 times of rated line current.a)2.3 Ωb)0.641 Ωc)5.17 Ωd)8.34 ΩCorrect answer is option 'C'. Can you explain this answer? has been provided alongside types of A 15 MVA, 11 kV, alternator has positive, negative and zero sequence reactance are 0.3 p.u., 0.2 p.u. and 0.05 p.u. respectively. Find the value of resistance to be added in the generator neutral so that the fault current of LG fault does not exceed 1.5 times of rated line current.a)2.3 Ωb)0.641 Ωc)5.17 Ωd)8.34 ΩCorrect answer is option 'C'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A 15 MVA, 11 kV, alternator has positive, negative and zero sequence reactance are 0.3 p.u., 0.2 p.u. and 0.05 p.u. respectively. Find the value of resistance to be added in the generator neutral so that the fault current of LG fault does not exceed 1.5 times of rated line current.a)2.3 Ωb)0.641 Ωc)5.17 Ωd)8.34 ΩCorrect answer is option 'C'. Can you explain this answer? tests, examples and also practice GATE tests.
Explore Courses for GATE exam
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev