ABCD parameters of 3 φ transmission line are A = D = 0.9∠2.5 °, B = 150∠81 °Ω and C = 0.05∠92.6 °S. If the sending end voltage is 450 kV, then the receiving end voltage under no load condition is _______ kV.
Correct answer is '500'. Can you explain this answer?
Verified Answer
ABCD parameters of 3 φ transmission line are A = D = 0.9∠2.5 °, B = 1...
View all questions of this test
Most Upvoted Answer
ABCD parameters of 3 φ transmission line are A = D = 0.9∠2.5 °, B = 1...
Given data:
- A = D = 0.9∠2.5°
- B = 150∠81° Ω
- C = 0.05∠92.6° S
- Sending end voltage = 450 kV

Calculation:

Step 1: Calculation of the transmission line parameters

We know that ABCD parameters of a transmission line are given by:

A = D = Z0 + Y0/2
B = Z0 - Y0/2
C = Y0/2 - Z0
D = Y0/2 + Z0

Where,
- A, B, C, D are the ABCD parameters
- Z0 is the characteristic impedance
- Y0 is the admittance

Given A = D = 0.9∠2.5° and C = 0.05∠92.6°S

From A = D, we get Z0 + Y0/2 = 0.9∠2.5°
From C, we get Y0/2 - Z0 = 0.05∠92.6°

Adding the above two equations, we get:
2Y0/2 = 0.95∠92.6°

Therefore, Y0 = 0.95∠92.6° S

Substituting the value of Y0 in the first equation, we get:
Z0 + 0.95∠92.6°/2 = 0.9∠2.5°

Simplifying the equation, we get:
Z0 = 0.9∠2.5° - 0.95∠92.6°/2
= 0.9∠2.5° - 0.475∠92.6°
= 0.9∠2.5° - 0.475∠92.6°

Step 2: Calculation of receiving end voltage

The receiving end voltage is given by:
Vr = Vs * (A + BZl)/(C + DZl)

Where,
- Vr is the receiving end voltage
- Vs is the sending end voltage
- Zl is the load impedance

Under no-load condition, the load impedance Zl is infinite. Therefore, Zl = ∞.

Substituting the values of A, B, C, D, and Zl in the above equation, we get:
Vr = Vs * (0.9∠2.5° + (150∠81° Ω)(∞))/(0.05∠92.6°S + (0.9∠2.5°)(∞))

Since Zl = ∞, the second term in the numerator and denominator becomes zero.

Vr = Vs * (0.9∠2.5°)/(0.05∠92.6°S)

Substituting the value of Vs = 450 kV, we get:
Vr = 450 * (0.9∠2.5°)/(0.05∠92.6°)

Simplifying the equation, we get:
Vr = 500 kV

Therefore, the receiving end voltage under no-load
Free Test
Community Answer
ABCD parameters of 3 φ transmission line are A = D = 0.9∠2.5 °, B = 1...
Vs=AVr+BIr
Is=CVr+Dlr
at no load condition lr=0
so
Vs=AVr
so Vr= 450 ÷0.9
= 500
Explore Courses for GATE exam

Similar GATE Doubts

ABCD parameters of 3 φ transmission line are A = D = 0.9∠2.5 °, B = 150∠81 °Ω and C = 0.05∠92.6 °S. If the sending end voltage is 450 kV, then the receiving end voltage under no load condition is _______ kV.Correct answer is '500'. Can you explain this answer?
Question Description
ABCD parameters of 3 φ transmission line are A = D = 0.9∠2.5 °, B = 150∠81 °Ω and C = 0.05∠92.6 °S. If the sending end voltage is 450 kV, then the receiving end voltage under no load condition is _______ kV.Correct answer is '500'. Can you explain this answer? for GATE 2024 is part of GATE preparation. The Question and answers have been prepared according to the GATE exam syllabus. Information about ABCD parameters of 3 φ transmission line are A = D = 0.9∠2.5 °, B = 150∠81 °Ω and C = 0.05∠92.6 °S. If the sending end voltage is 450 kV, then the receiving end voltage under no load condition is _______ kV.Correct answer is '500'. Can you explain this answer? covers all topics & solutions for GATE 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for ABCD parameters of 3 φ transmission line are A = D = 0.9∠2.5 °, B = 150∠81 °Ω and C = 0.05∠92.6 °S. If the sending end voltage is 450 kV, then the receiving end voltage under no load condition is _______ kV.Correct answer is '500'. Can you explain this answer?.
Solutions for ABCD parameters of 3 φ transmission line are A = D = 0.9∠2.5 °, B = 150∠81 °Ω and C = 0.05∠92.6 °S. If the sending end voltage is 450 kV, then the receiving end voltage under no load condition is _______ kV.Correct answer is '500'. Can you explain this answer? in English & in Hindi are available as part of our courses for GATE. Download more important topics, notes, lectures and mock test series for GATE Exam by signing up for free.
Here you can find the meaning of ABCD parameters of 3 φ transmission line are A = D = 0.9∠2.5 °, B = 150∠81 °Ω and C = 0.05∠92.6 °S. If the sending end voltage is 450 kV, then the receiving end voltage under no load condition is _______ kV.Correct answer is '500'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of ABCD parameters of 3 φ transmission line are A = D = 0.9∠2.5 °, B = 150∠81 °Ω and C = 0.05∠92.6 °S. If the sending end voltage is 450 kV, then the receiving end voltage under no load condition is _______ kV.Correct answer is '500'. Can you explain this answer?, a detailed solution for ABCD parameters of 3 φ transmission line are A = D = 0.9∠2.5 °, B = 150∠81 °Ω and C = 0.05∠92.6 °S. If the sending end voltage is 450 kV, then the receiving end voltage under no load condition is _______ kV.Correct answer is '500'. Can you explain this answer? has been provided alongside types of ABCD parameters of 3 φ transmission line are A = D = 0.9∠2.5 °, B = 150∠81 °Ω and C = 0.05∠92.6 °S. If the sending end voltage is 450 kV, then the receiving end voltage under no load condition is _______ kV.Correct answer is '500'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice ABCD parameters of 3 φ transmission line are A = D = 0.9∠2.5 °, B = 150∠81 °Ω and C = 0.05∠92.6 °S. If the sending end voltage is 450 kV, then the receiving end voltage under no load condition is _______ kV.Correct answer is '500'. Can you explain this answer? tests, examples and also practice GATE tests.
Explore Courses for GATE exam
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev