Two power plants interconnected by a tie-line as shown in the below figure have loss formula coefficient B11 = 10–3 MW–1. Power is being dispatched economically with plant ‘1’ as 100 MW and plant ‘2’ as 125 MW. The penality factor for plants 1 and 2 are respectively.
  • a)
    1 and 1.25
  • b)
    1.25 and 1
  • c)
    1 and zero
  • d)
    zero and 1
Correct answer is option 'B'. Can you explain this answer?
Verified Answer
Two power plants interconnected by a tie-line as shown in the below f...
Since the load is at the bus of plant -2, therefore B12=B21=0 and B22=0 for a 2 -plant system
Penality factor of Plant-1
Similarly,
Penality factor of Plant-2 L2
View all questions of this test
Most Upvoted Answer
Two power plants interconnected by a tie-line as shown in the below f...
Since the load is at the bus of plant -2, therefore B12=B21=0 and B22=0 for a 2 -plant system
Penality factor of Plant-1
Similarly,
Penality factor of Plant-2 L2
Explore Courses for GATE exam

Similar GATE Doubts

Two power plants interconnected by a tie-line as shown in the below figure have loss formula coefficient B11 = 10–3 MW–1. Power is being dispatched economically with plant ‘1’ as 100 MW and plant ‘2’ as 125 MW. The penality factor for plants 1 and 2 are respectively.a)1 and 1.25b)1.25 and 1c)1 and zerod)zero and 1Correct answer is option 'B'. Can you explain this answer?
Question Description
Two power plants interconnected by a tie-line as shown in the below figure have loss formula coefficient B11 = 10–3 MW–1. Power is being dispatched economically with plant ‘1’ as 100 MW and plant ‘2’ as 125 MW. The penality factor for plants 1 and 2 are respectively.a)1 and 1.25b)1.25 and 1c)1 and zerod)zero and 1Correct answer is option 'B'. Can you explain this answer? for GATE 2025 is part of GATE preparation. The Question and answers have been prepared according to the GATE exam syllabus. Information about Two power plants interconnected by a tie-line as shown in the below figure have loss formula coefficient B11 = 10–3 MW–1. Power is being dispatched economically with plant ‘1’ as 100 MW and plant ‘2’ as 125 MW. The penality factor for plants 1 and 2 are respectively.a)1 and 1.25b)1.25 and 1c)1 and zerod)zero and 1Correct answer is option 'B'. Can you explain this answer? covers all topics & solutions for GATE 2025 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for Two power plants interconnected by a tie-line as shown in the below figure have loss formula coefficient B11 = 10–3 MW–1. Power is being dispatched economically with plant ‘1’ as 100 MW and plant ‘2’ as 125 MW. The penality factor for plants 1 and 2 are respectively.a)1 and 1.25b)1.25 and 1c)1 and zerod)zero and 1Correct answer is option 'B'. Can you explain this answer?.
Solutions for Two power plants interconnected by a tie-line as shown in the below figure have loss formula coefficient B11 = 10–3 MW–1. Power is being dispatched economically with plant ‘1’ as 100 MW and plant ‘2’ as 125 MW. The penality factor for plants 1 and 2 are respectively.a)1 and 1.25b)1.25 and 1c)1 and zerod)zero and 1Correct answer is option 'B'. Can you explain this answer? in English & in Hindi are available as part of our courses for GATE. Download more important topics, notes, lectures and mock test series for GATE Exam by signing up for free.
Here you can find the meaning of Two power plants interconnected by a tie-line as shown in the below figure have loss formula coefficient B11 = 10–3 MW–1. Power is being dispatched economically with plant ‘1’ as 100 MW and plant ‘2’ as 125 MW. The penality factor for plants 1 and 2 are respectively.a)1 and 1.25b)1.25 and 1c)1 and zerod)zero and 1Correct answer is option 'B'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of Two power plants interconnected by a tie-line as shown in the below figure have loss formula coefficient B11 = 10–3 MW–1. Power is being dispatched economically with plant ‘1’ as 100 MW and plant ‘2’ as 125 MW. The penality factor for plants 1 and 2 are respectively.a)1 and 1.25b)1.25 and 1c)1 and zerod)zero and 1Correct answer is option 'B'. Can you explain this answer?, a detailed solution for Two power plants interconnected by a tie-line as shown in the below figure have loss formula coefficient B11 = 10–3 MW–1. Power is being dispatched economically with plant ‘1’ as 100 MW and plant ‘2’ as 125 MW. The penality factor for plants 1 and 2 are respectively.a)1 and 1.25b)1.25 and 1c)1 and zerod)zero and 1Correct answer is option 'B'. Can you explain this answer? has been provided alongside types of Two power plants interconnected by a tie-line as shown in the below figure have loss formula coefficient B11 = 10–3 MW–1. Power is being dispatched economically with plant ‘1’ as 100 MW and plant ‘2’ as 125 MW. The penality factor for plants 1 and 2 are respectively.a)1 and 1.25b)1.25 and 1c)1 and zerod)zero and 1Correct answer is option 'B'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice Two power plants interconnected by a tie-line as shown in the below figure have loss formula coefficient B11 = 10–3 MW–1. Power is being dispatched economically with plant ‘1’ as 100 MW and plant ‘2’ as 125 MW. The penality factor for plants 1 and 2 are respectively.a)1 and 1.25b)1.25 and 1c)1 and zerod)zero and 1Correct answer is option 'B'. Can you explain this answer? tests, examples and also practice GATE tests.
Explore Courses for GATE exam
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev