GATE Exam  >  GATE Questions  >  Moist air at 105 kPa, 30°C and 80% relati... Start Learning for Free
Moist air at 105 kPa, 30°C and 80% relative humidity flows over a cooling coil in an insulated air-conditioning duct. Saturated air exits the duct at 100 kPa and 15°C. The saturation pressure of water at 30°C and 15°C are 4.24 kPa and 1.7 kPa respectively.
Molecular weight of water is 18 g/mol and that of air is 28.94 g/mol. The mass of water condensing out from the duct is ______ g/kg of dry air (round off to 2 decimal places).
    Correct answer is '10'. Can you explain this answer?
    Verified Answer
    Moist air at 105 kPa, 30°C and 80% relative humidity flows over a ...
    Pt1 = 105 kPa, DBT1 = 30°C, φ1 = 0.8 Pt2 = 100 kPa, DBT2 = 15°C, φ2 = 1 Pvs1 = 4.24 kPa
    Pvs2 = 1.7 kPa
    Mwater = 18 g/mol.
    Mair = 28.94 g/mol.




    ∴ Pv1 = 3.392
    ∴ 
    = 20.76 gv/kgd.a


    ∴ Pv2 = 1.7
    ∴ 
    Mass of water condensing = ω1 – ω2 = 20.76 – 10.75
    = 10.01 g/kgd.a
    View all questions of this test
    Most Upvoted Answer
    Moist air at 105 kPa, 30°C and 80% relative humidity flows over a ...
    The question seems to be incomplete. Please provide more information so that I can properly assist you.
    Explore Courses for GATE exam

    Similar GATE Doubts

    Moist air at 105 kPa, 30°C and 80% relative humidity flows over a cooling coil in an insulated air-conditioning duct. Saturated air exits the duct at 100 kPa and 15°C. The saturation pressure of water at 30°C and 15°C are 4.24 kPa and 1.7 kPa respectively.Molecular weight of water is 18 g/mol and that of air is 28.94 g/mol. The mass of water condensing out from the duct is ______ g/kg of dry air (round off to 2 decimal places).Correct answer is '10'. Can you explain this answer?
    Question Description
    Moist air at 105 kPa, 30°C and 80% relative humidity flows over a cooling coil in an insulated air-conditioning duct. Saturated air exits the duct at 100 kPa and 15°C. The saturation pressure of water at 30°C and 15°C are 4.24 kPa and 1.7 kPa respectively.Molecular weight of water is 18 g/mol and that of air is 28.94 g/mol. The mass of water condensing out from the duct is ______ g/kg of dry air (round off to 2 decimal places).Correct answer is '10'. Can you explain this answer? for GATE 2024 is part of GATE preparation. The Question and answers have been prepared according to the GATE exam syllabus. Information about Moist air at 105 kPa, 30°C and 80% relative humidity flows over a cooling coil in an insulated air-conditioning duct. Saturated air exits the duct at 100 kPa and 15°C. The saturation pressure of water at 30°C and 15°C are 4.24 kPa and 1.7 kPa respectively.Molecular weight of water is 18 g/mol and that of air is 28.94 g/mol. The mass of water condensing out from the duct is ______ g/kg of dry air (round off to 2 decimal places).Correct answer is '10'. Can you explain this answer? covers all topics & solutions for GATE 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for Moist air at 105 kPa, 30°C and 80% relative humidity flows over a cooling coil in an insulated air-conditioning duct. Saturated air exits the duct at 100 kPa and 15°C. The saturation pressure of water at 30°C and 15°C are 4.24 kPa and 1.7 kPa respectively.Molecular weight of water is 18 g/mol and that of air is 28.94 g/mol. The mass of water condensing out from the duct is ______ g/kg of dry air (round off to 2 decimal places).Correct answer is '10'. Can you explain this answer?.
    Solutions for Moist air at 105 kPa, 30°C and 80% relative humidity flows over a cooling coil in an insulated air-conditioning duct. Saturated air exits the duct at 100 kPa and 15°C. The saturation pressure of water at 30°C and 15°C are 4.24 kPa and 1.7 kPa respectively.Molecular weight of water is 18 g/mol and that of air is 28.94 g/mol. The mass of water condensing out from the duct is ______ g/kg of dry air (round off to 2 decimal places).Correct answer is '10'. Can you explain this answer? in English & in Hindi are available as part of our courses for GATE. Download more important topics, notes, lectures and mock test series for GATE Exam by signing up for free.
    Here you can find the meaning of Moist air at 105 kPa, 30°C and 80% relative humidity flows over a cooling coil in an insulated air-conditioning duct. Saturated air exits the duct at 100 kPa and 15°C. The saturation pressure of water at 30°C and 15°C are 4.24 kPa and 1.7 kPa respectively.Molecular weight of water is 18 g/mol and that of air is 28.94 g/mol. The mass of water condensing out from the duct is ______ g/kg of dry air (round off to 2 decimal places).Correct answer is '10'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of Moist air at 105 kPa, 30°C and 80% relative humidity flows over a cooling coil in an insulated air-conditioning duct. Saturated air exits the duct at 100 kPa and 15°C. The saturation pressure of water at 30°C and 15°C are 4.24 kPa and 1.7 kPa respectively.Molecular weight of water is 18 g/mol and that of air is 28.94 g/mol. The mass of water condensing out from the duct is ______ g/kg of dry air (round off to 2 decimal places).Correct answer is '10'. Can you explain this answer?, a detailed solution for Moist air at 105 kPa, 30°C and 80% relative humidity flows over a cooling coil in an insulated air-conditioning duct. Saturated air exits the duct at 100 kPa and 15°C. The saturation pressure of water at 30°C and 15°C are 4.24 kPa and 1.7 kPa respectively.Molecular weight of water is 18 g/mol and that of air is 28.94 g/mol. The mass of water condensing out from the duct is ______ g/kg of dry air (round off to 2 decimal places).Correct answer is '10'. Can you explain this answer? has been provided alongside types of Moist air at 105 kPa, 30°C and 80% relative humidity flows over a cooling coil in an insulated air-conditioning duct. Saturated air exits the duct at 100 kPa and 15°C. The saturation pressure of water at 30°C and 15°C are 4.24 kPa and 1.7 kPa respectively.Molecular weight of water is 18 g/mol and that of air is 28.94 g/mol. The mass of water condensing out from the duct is ______ g/kg of dry air (round off to 2 decimal places).Correct answer is '10'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice Moist air at 105 kPa, 30°C and 80% relative humidity flows over a cooling coil in an insulated air-conditioning duct. Saturated air exits the duct at 100 kPa and 15°C. The saturation pressure of water at 30°C and 15°C are 4.24 kPa and 1.7 kPa respectively.Molecular weight of water is 18 g/mol and that of air is 28.94 g/mol. The mass of water condensing out from the duct is ______ g/kg of dry air (round off to 2 decimal places).Correct answer is '10'. Can you explain this answer? tests, examples and also practice GATE tests.
    Explore Courses for GATE exam
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev