The positive negative and zero sequence impedances of the 3-phase synchronous generator are j 0.5 pu, j 0.3 pu and j 0.2 pu, respectively. When a symmetrical fault occurs on the machine terminals. Find the fault current. The generator neutral is grounded through reactance of j0.1 pu-
  • a)
    (-j33.33pu)
  • b)
    (-j1.67pu)
  • c)
    (-j2.0pu)
  • d)
    (-j2.5pu)
Correct answer is option 'B'. Can you explain this answer?
Verified Answer
The positive negative and zero sequence impedances of the 3-phase syn...
For symmetrical fault,
View all questions of this test
Most Upvoted Answer
The positive negative and zero sequence impedances of the 3-phase syn...
Given:
Positive sequence impedance (Z1) = j0.5 pu
Negative sequence impedance (Z2) = j0.3 pu
Zero sequence impedance (Z0) = j0.2 pu
Reactance of generator neutral grounding (Xn) = j0.1 pu

To Find:
Fault current

Explanation:
The fault current can be calculated using the following formula:

If = (Va - Vf) / (Z1 + Z2 + Z0 + 3*Xn)

Where:
If = Fault current
Va = Generator terminal voltage
Vf = Fault voltage

Since it is mentioned that a symmetrical fault occurs on the machine terminals, the fault voltage (Vf) will be equal to the generator terminal voltage (Va).

Substituting the given values:
Va = Vf

If = (Va - Va) / (Z1 + Z2 + Z0 + 3*Xn)
= 0 / (Z1 + Z2 + Z0 + 3*Xn)
= 0 / (j0.5 + j0.3 + j0.2 + 3*j0.1)
= 0 / (j0.5 + j0.3 + j0.2 + j0.3)
= 0 / (j1 + j0.5)
= 0 / j1.5
= 0

Therefore, the fault current is 0.

Conclusion:
The fault current in the given scenario is 0.
Explore Courses for SSC exam

Similar SSC Doubts

The positive negative and zero sequence impedances of the 3-phase synchronous generator are j 0.5 pu, j 0.3 pu and j 0.2 pu, respectively. When a symmetrical fault occurs on the machine terminals. Find the fault current. The generator neutral is grounded through reactance of j0.1 pu-a)(-j33.33pu)b)(-j1.67pu)c)(-j2.0pu)d)(-j2.5pu)Correct answer is option 'B'. Can you explain this answer?
Question Description
The positive negative and zero sequence impedances of the 3-phase synchronous generator are j 0.5 pu, j 0.3 pu and j 0.2 pu, respectively. When a symmetrical fault occurs on the machine terminals. Find the fault current. The generator neutral is grounded through reactance of j0.1 pu-a)(-j33.33pu)b)(-j1.67pu)c)(-j2.0pu)d)(-j2.5pu)Correct answer is option 'B'. Can you explain this answer? for SSC 2024 is part of SSC preparation. The Question and answers have been prepared according to the SSC exam syllabus. Information about The positive negative and zero sequence impedances of the 3-phase synchronous generator are j 0.5 pu, j 0.3 pu and j 0.2 pu, respectively. When a symmetrical fault occurs on the machine terminals. Find the fault current. The generator neutral is grounded through reactance of j0.1 pu-a)(-j33.33pu)b)(-j1.67pu)c)(-j2.0pu)d)(-j2.5pu)Correct answer is option 'B'. Can you explain this answer? covers all topics & solutions for SSC 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for The positive negative and zero sequence impedances of the 3-phase synchronous generator are j 0.5 pu, j 0.3 pu and j 0.2 pu, respectively. When a symmetrical fault occurs on the machine terminals. Find the fault current. The generator neutral is grounded through reactance of j0.1 pu-a)(-j33.33pu)b)(-j1.67pu)c)(-j2.0pu)d)(-j2.5pu)Correct answer is option 'B'. Can you explain this answer?.
Solutions for The positive negative and zero sequence impedances of the 3-phase synchronous generator are j 0.5 pu, j 0.3 pu and j 0.2 pu, respectively. When a symmetrical fault occurs on the machine terminals. Find the fault current. The generator neutral is grounded through reactance of j0.1 pu-a)(-j33.33pu)b)(-j1.67pu)c)(-j2.0pu)d)(-j2.5pu)Correct answer is option 'B'. Can you explain this answer? in English & in Hindi are available as part of our courses for SSC. Download more important topics, notes, lectures and mock test series for SSC Exam by signing up for free.
Here you can find the meaning of The positive negative and zero sequence impedances of the 3-phase synchronous generator are j 0.5 pu, j 0.3 pu and j 0.2 pu, respectively. When a symmetrical fault occurs on the machine terminals. Find the fault current. The generator neutral is grounded through reactance of j0.1 pu-a)(-j33.33pu)b)(-j1.67pu)c)(-j2.0pu)d)(-j2.5pu)Correct answer is option 'B'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of The positive negative and zero sequence impedances of the 3-phase synchronous generator are j 0.5 pu, j 0.3 pu and j 0.2 pu, respectively. When a symmetrical fault occurs on the machine terminals. Find the fault current. The generator neutral is grounded through reactance of j0.1 pu-a)(-j33.33pu)b)(-j1.67pu)c)(-j2.0pu)d)(-j2.5pu)Correct answer is option 'B'. Can you explain this answer?, a detailed solution for The positive negative and zero sequence impedances of the 3-phase synchronous generator are j 0.5 pu, j 0.3 pu and j 0.2 pu, respectively. When a symmetrical fault occurs on the machine terminals. Find the fault current. The generator neutral is grounded through reactance of j0.1 pu-a)(-j33.33pu)b)(-j1.67pu)c)(-j2.0pu)d)(-j2.5pu)Correct answer is option 'B'. Can you explain this answer? has been provided alongside types of The positive negative and zero sequence impedances of the 3-phase synchronous generator are j 0.5 pu, j 0.3 pu and j 0.2 pu, respectively. When a symmetrical fault occurs on the machine terminals. Find the fault current. The generator neutral is grounded through reactance of j0.1 pu-a)(-j33.33pu)b)(-j1.67pu)c)(-j2.0pu)d)(-j2.5pu)Correct answer is option 'B'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice The positive negative and zero sequence impedances of the 3-phase synchronous generator are j 0.5 pu, j 0.3 pu and j 0.2 pu, respectively. When a symmetrical fault occurs on the machine terminals. Find the fault current. The generator neutral is grounded through reactance of j0.1 pu-a)(-j33.33pu)b)(-j1.67pu)c)(-j2.0pu)d)(-j2.5pu)Correct answer is option 'B'. Can you explain this answer? tests, examples and also practice SSC tests.
Explore Courses for SSC exam
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev