Calculate the time of operation of an IDMT type over-current relay is used to protect a feeder through 400/1 ACT, relay has plug setting of 125٪ and TMS =0.6 and fault current is 4000 A . Use the following characteristic.
  • a)
    1.96 sec
  • b)
    1.97 sec
  • c)
    1.98 sec
  • d)
    1.99 sec
Correct answer is option 'C'. Can you explain this answer?
Verified Answer
Calculate the time of operation of an IDMT type over-current relay is ...
Given, plug setting =125%
TMS=O.G
Fault current, If=4000A
Pick up current, I PK= plug setting × C.T. secondary current=1.25×1=1.25
Plug Setting multiplier,
Now, time of operation of any relay,
T=TMS x (Time calculated from IDMT table corresponding)
T = 0.6 x 3.3 = 1.98 sec
View all questions of this test
Most Upvoted Answer
Calculate the time of operation of an IDMT type over-current relay is ...
Given, plug setting =125%
TMS=O.G
Fault current, If=4000A
Pick up current, I PK= plug setting × C.T. secondary current=1.25×1=1.25
Plug Setting multiplier,
Now, time of operation of any relay,
T=TMS x (Time calculated from IDMT table corresponding)
T = 0.6 x 3.3 = 1.98 sec
Explore Courses for GATE exam

Similar GATE Doubts

Calculate the time of operation of an IDMT type over-current relay is used to protect a feeder through 400/1 ACT, relay has plug setting of 125 and TMS =0.6 and fault current is 4000 A . Use the following characteristic.a)1.96 secb)1.97 secc)1.98 secd)1.99 secCorrect answer is option 'C'. Can you explain this answer?
Question Description
Calculate the time of operation of an IDMT type over-current relay is used to protect a feeder through 400/1 ACT, relay has plug setting of 125 and TMS =0.6 and fault current is 4000 A . Use the following characteristic.a)1.96 secb)1.97 secc)1.98 secd)1.99 secCorrect answer is option 'C'. Can you explain this answer? for GATE 2024 is part of GATE preparation. The Question and answers have been prepared according to the GATE exam syllabus. Information about Calculate the time of operation of an IDMT type over-current relay is used to protect a feeder through 400/1 ACT, relay has plug setting of 125 and TMS =0.6 and fault current is 4000 A . Use the following characteristic.a)1.96 secb)1.97 secc)1.98 secd)1.99 secCorrect answer is option 'C'. Can you explain this answer? covers all topics & solutions for GATE 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for Calculate the time of operation of an IDMT type over-current relay is used to protect a feeder through 400/1 ACT, relay has plug setting of 125 and TMS =0.6 and fault current is 4000 A . Use the following characteristic.a)1.96 secb)1.97 secc)1.98 secd)1.99 secCorrect answer is option 'C'. Can you explain this answer?.
Solutions for Calculate the time of operation of an IDMT type over-current relay is used to protect a feeder through 400/1 ACT, relay has plug setting of 125 and TMS =0.6 and fault current is 4000 A . Use the following characteristic.a)1.96 secb)1.97 secc)1.98 secd)1.99 secCorrect answer is option 'C'. Can you explain this answer? in English & in Hindi are available as part of our courses for GATE. Download more important topics, notes, lectures and mock test series for GATE Exam by signing up for free.
Here you can find the meaning of Calculate the time of operation of an IDMT type over-current relay is used to protect a feeder through 400/1 ACT, relay has plug setting of 125 and TMS =0.6 and fault current is 4000 A . Use the following characteristic.a)1.96 secb)1.97 secc)1.98 secd)1.99 secCorrect answer is option 'C'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of Calculate the time of operation of an IDMT type over-current relay is used to protect a feeder through 400/1 ACT, relay has plug setting of 125 and TMS =0.6 and fault current is 4000 A . Use the following characteristic.a)1.96 secb)1.97 secc)1.98 secd)1.99 secCorrect answer is option 'C'. Can you explain this answer?, a detailed solution for Calculate the time of operation of an IDMT type over-current relay is used to protect a feeder through 400/1 ACT, relay has plug setting of 125 and TMS =0.6 and fault current is 4000 A . Use the following characteristic.a)1.96 secb)1.97 secc)1.98 secd)1.99 secCorrect answer is option 'C'. Can you explain this answer? has been provided alongside types of Calculate the time of operation of an IDMT type over-current relay is used to protect a feeder through 400/1 ACT, relay has plug setting of 125 and TMS =0.6 and fault current is 4000 A . Use the following characteristic.a)1.96 secb)1.97 secc)1.98 secd)1.99 secCorrect answer is option 'C'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice Calculate the time of operation of an IDMT type over-current relay is used to protect a feeder through 400/1 ACT, relay has plug setting of 125 and TMS =0.6 and fault current is 4000 A . Use the following characteristic.a)1.96 secb)1.97 secc)1.98 secd)1.99 secCorrect answer is option 'C'. Can you explain this answer? tests, examples and also practice GATE tests.
Explore Courses for GATE exam
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev