A generator rated 100 k V A 13.8 kV and having reactance x1 = x2 = 0.1 p.u. and x0 = 0.05 p.u. its neutral being grounded through a current reactor of 0.08 pu. The generator is connected to a connected step up transformer with 0.06 p.u. reactance its neutral being solidly grounded. A double line to ground fault occurs at star side of transformer. Calculate fault current in p.u.
  • a)
    6.71 p.u.
  • b)
    0.71 p.u.
  • c)
    9.71 p.u.
  • d)
    11.71 p.u.
Correct answer is option 'B'. Can you explain this answer?
Verified Answer
A generator rated 100 k V A 13.8 kV and having reactance x1 = x2 = 0....
+ve sequence n/w is
-ve sequence n/w is
Zero sequence n/w
Fault current
|If|=3|Ifo|
= 3 x 3.57
= 10.71 p.u.
View all questions of this test
Most Upvoted Answer
A generator rated 100 k V A 13.8 kV and having reactance x1 = x2 = 0....
Calculation of Fault Current in a Generator-Transformer System

Given Data:
Generator rating = 100 kVA
Generator voltage = 13.8 kV
Reactance of generator (x1 = x2) = 0.1 p.u.
Zero sequence reactance of generator (x0) = 0.05 p.u.
Current reactor reactance = 0.08 p.u.
Transformer reactance = 0.06 p.u.
Fault type = Double line to ground fault
Neutral grounding of generator = through a current reactor
Neutral grounding of transformer = solidly grounded

Step 1: Calculation of per unit values
Base kVA = 100 kVA
Base kV = 13.8 kV
Base impedance = (Base kV)^2 / Base kVA = 13.8^2 / 100 = 1.896 ohms
Per unit impedance (p.u.) = Actual impedance / Base impedance

Reactance of generator (x1 = x2) = 0.1 p.u.
Zero sequence reactance of generator (x0) = 0.05 p.u.
Current reactor reactance = 0.08 p.u.
Transformer reactance = 0.06 p.u.

Step 2: Calculation of equivalent circuit
The equivalent circuit for the generator-transformer system during a double line to ground fault is as follows:

Xeq = [(x1 + x0)/3 + 3x2] + (2x0/3) + (2x1/3) + Xtr
Xeq = [(0.1 + 0.05)/3 + 3(0.1)] + (2*0.05/3) + (2*0.1/3) + 0.06
Xeq = 0.4817 p.u.

Step 3: Calculation of fault current
The fault current in the generator-transformer system can be calculated using the following equation:

Ifault = Vg / (3Xeq + X0)
where Vg is the generator voltage

Ifault = 13.8 kV / [3(0.4817) + 0.05]
Ifault = 0.71 p.u.

Therefore, the fault current in the generator-transformer system during a double line to ground fault is 0.71 p.u. Option B is the correct answer.
Explore Courses for GATE exam
A generator rated 100 k V A 13.8 kV and having reactance x1 = x2 = 0.1 p.u. and x0 = 0.05 p.u. its neutral being grounded through a current reactor of 0.08 pu. The generator is connected to a connected step up transformer with 0.06 p.u. reactance its neutral being solidly grounded. A double line to ground fault occurs at star side of transformer. Calculate fault current in p.u.a)6.71 p.u.b)0.71 p.u.c)9.71 p.u.d)11.71 p.u.Correct answer is option 'B'. Can you explain this answer?
Question Description
A generator rated 100 k V A 13.8 kV and having reactance x1 = x2 = 0.1 p.u. and x0 = 0.05 p.u. its neutral being grounded through a current reactor of 0.08 pu. The generator is connected to a connected step up transformer with 0.06 p.u. reactance its neutral being solidly grounded. A double line to ground fault occurs at star side of transformer. Calculate fault current in p.u.a)6.71 p.u.b)0.71 p.u.c)9.71 p.u.d)11.71 p.u.Correct answer is option 'B'. Can you explain this answer? for GATE 2024 is part of GATE preparation. The Question and answers have been prepared according to the GATE exam syllabus. Information about A generator rated 100 k V A 13.8 kV and having reactance x1 = x2 = 0.1 p.u. and x0 = 0.05 p.u. its neutral being grounded through a current reactor of 0.08 pu. The generator is connected to a connected step up transformer with 0.06 p.u. reactance its neutral being solidly grounded. A double line to ground fault occurs at star side of transformer. Calculate fault current in p.u.a)6.71 p.u.b)0.71 p.u.c)9.71 p.u.d)11.71 p.u.Correct answer is option 'B'. Can you explain this answer? covers all topics & solutions for GATE 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A generator rated 100 k V A 13.8 kV and having reactance x1 = x2 = 0.1 p.u. and x0 = 0.05 p.u. its neutral being grounded through a current reactor of 0.08 pu. The generator is connected to a connected step up transformer with 0.06 p.u. reactance its neutral being solidly grounded. A double line to ground fault occurs at star side of transformer. Calculate fault current in p.u.a)6.71 p.u.b)0.71 p.u.c)9.71 p.u.d)11.71 p.u.Correct answer is option 'B'. Can you explain this answer?.
Solutions for A generator rated 100 k V A 13.8 kV and having reactance x1 = x2 = 0.1 p.u. and x0 = 0.05 p.u. its neutral being grounded through a current reactor of 0.08 pu. The generator is connected to a connected step up transformer with 0.06 p.u. reactance its neutral being solidly grounded. A double line to ground fault occurs at star side of transformer. Calculate fault current in p.u.a)6.71 p.u.b)0.71 p.u.c)9.71 p.u.d)11.71 p.u.Correct answer is option 'B'. Can you explain this answer? in English & in Hindi are available as part of our courses for GATE. Download more important topics, notes, lectures and mock test series for GATE Exam by signing up for free.
Here you can find the meaning of A generator rated 100 k V A 13.8 kV and having reactance x1 = x2 = 0.1 p.u. and x0 = 0.05 p.u. its neutral being grounded through a current reactor of 0.08 pu. The generator is connected to a connected step up transformer with 0.06 p.u. reactance its neutral being solidly grounded. A double line to ground fault occurs at star side of transformer. Calculate fault current in p.u.a)6.71 p.u.b)0.71 p.u.c)9.71 p.u.d)11.71 p.u.Correct answer is option 'B'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A generator rated 100 k V A 13.8 kV and having reactance x1 = x2 = 0.1 p.u. and x0 = 0.05 p.u. its neutral being grounded through a current reactor of 0.08 pu. The generator is connected to a connected step up transformer with 0.06 p.u. reactance its neutral being solidly grounded. A double line to ground fault occurs at star side of transformer. Calculate fault current in p.u.a)6.71 p.u.b)0.71 p.u.c)9.71 p.u.d)11.71 p.u.Correct answer is option 'B'. Can you explain this answer?, a detailed solution for A generator rated 100 k V A 13.8 kV and having reactance x1 = x2 = 0.1 p.u. and x0 = 0.05 p.u. its neutral being grounded through a current reactor of 0.08 pu. The generator is connected to a connected step up transformer with 0.06 p.u. reactance its neutral being solidly grounded. A double line to ground fault occurs at star side of transformer. Calculate fault current in p.u.a)6.71 p.u.b)0.71 p.u.c)9.71 p.u.d)11.71 p.u.Correct answer is option 'B'. Can you explain this answer? has been provided alongside types of A generator rated 100 k V A 13.8 kV and having reactance x1 = x2 = 0.1 p.u. and x0 = 0.05 p.u. its neutral being grounded through a current reactor of 0.08 pu. The generator is connected to a connected step up transformer with 0.06 p.u. reactance its neutral being solidly grounded. A double line to ground fault occurs at star side of transformer. Calculate fault current in p.u.a)6.71 p.u.b)0.71 p.u.c)9.71 p.u.d)11.71 p.u.Correct answer is option 'B'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A generator rated 100 k V A 13.8 kV and having reactance x1 = x2 = 0.1 p.u. and x0 = 0.05 p.u. its neutral being grounded through a current reactor of 0.08 pu. The generator is connected to a connected step up transformer with 0.06 p.u. reactance its neutral being solidly grounded. A double line to ground fault occurs at star side of transformer. Calculate fault current in p.u.a)6.71 p.u.b)0.71 p.u.c)9.71 p.u.d)11.71 p.u.Correct answer is option 'B'. Can you explain this answer? tests, examples and also practice GATE tests.
Explore Courses for GATE exam
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev